Dear all Guru,
I hv an electrical heated oven which divide in to 4 heating zones (2.2m x width 3m x height 0.8m ,each zone) with total lenght of 8.8m, each zone is run by 170kw heater and connected to 3ph 415v + Nuetral power supply.(heater control by ON/OFF contactor only)
The starting all the heater will be on , so 170kw x 4 = 680kw
Now if i want to convert to Natural gas fired burner , gas pressure at 100mBar , pipe size 1 1/2".
Please adivse me what is the burner heating capacity for each zone ? and waht is max. gas flow speed in the pipe 1 1/2" ?
Thank You and Best Regards
Re: Electrical heater Vs Natural gas burner heating
03/23/2009 4:30 AM
What is the calorific value of the gas to be used?
03/23/2009 4:36 AM
Hi PWSlack,
NG CV is 9580kcal/sm³
Thanks
Good Answers: 137
03/23/2009 5:47 AM
aikhh
Electric heaters are 100% efficient as the element is in the oven you are heating. This is unlikely to be the case for gas heaters, but the efficiency depends on the arrangement and you need to discuss with the heater supplier. When you know that you can calculate the gas flow hence velocity in 1½" pipe.
Presumably you need a separate heater for each zone. Supplier will tell you connection size and minimum pressure requirement. You can then check whether your gas pipe and system are adequate.
Cheers......Codey