Signal

03/31/2009 5:14 AM

I want to tie some of the diagnostic alarm to our safeguarding PLC for predictive/proactive maintenance purpose.

Now, the question is, if the mA is between 2.51-2.99 mA, what should be the status. Is it dirty optic or block?

We cannot configure comparator in the logic such that it will only give dirty optic alarm when the signal =3 mA and alarm will be clear if the mA drop below 3 mA but still higher than 2.5 mA.Please help me On This.

E&I Engineer

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Signal

03/31/2009 5:25 AM

On the basis of what has been posted so far the logic goes along the lines of :

  • if (signal value < -6.25% of range) then (alarm condition 1) else (no alarm condition 1)
  • if (signal value < -9.375% of range) then (alarm condition 2) else (no alarm condition 2)

Then call out the instrument technician using the basis of the alarm conditions as guidance for that individual.