CAPACITOR CONNECTION TO VARIABLE-FREQUENCY DRIVE for Improving Power Factor.

04/05/2009 7:11 AM

We are having VARIABLE SPEED DRIVE in 5 different equipments

of varying capacity from 5 K.W to 160 K.W and 375 K.W.

Can we connect Power Capacitor after the VARIABL FREQUENCY DRIVE.

to IMPROVE THE POWER FACTOR. If not to to be connected after VFD Panel

What is the reason.? and What will happen if Capacitor is connected after the

VFD. My team says power capacitor to be connected before VFD, Is this right.

DHAYANANDHAN.S,

INDIA,

5-4-09

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#1

Re: CAPACITOR CONNECTION TO VARIABLE-FREQUENCY DRIVE for Improving Power Factor.

04/05/2009 11:55 AM

In VFD, the system AC is first converted to DC and then the DC is converted to AC which is supplied to the Motor. The intension of using the capacitor is to improve your system power factor. So, you have to use it before VFD.

Note: the capacitor is also used in DC part of VFD to filter the DC to make it smooth but you mentioned the use of capacitor is for PF improvement.

Hope it helps.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#2
In reply to #1

Re: CAPACITOR CONNECTION TO VARIABLE-FREQUENCY DRIVE for Improving Power Factor.

04/05/2009 12:30 PM

Dear Mr.MSAMAD,

Thank you for your reply.

The capacitor addition - It is for improving the Power Factor.

At higher speed hence higher Frequency, the Inductive Effect is more

and hence I am of the opinion that in order to compensate for the

fall in Power Factor, the Capacitor to be added close to the input supply

to the Motor and in this case of VFD. it is after the DC to AC conversion

to a higher frequency goes to the motor.

DHAYANANDHAN,

INDIA.

Register to Reply
5
Power-User
New Zealand - Member - Kiwi

Join Date: Oct 2007
Location: Christchurch, New Zealand
Posts: 328
Good Answers: 29
#3

Re: CAPACITOR CONNECTION TO VARIABLE-FREQUENCY DRIVE for Improving Power Factor.

04/05/2009 3:44 PM

You have asked if you can connect capacitors between a VFD and motor to improve the power factor. Not only will this have no effect on the power factor upstream of the VFD, it will also destroy the power switching components in the VFD, as they are not designed to cope with capacitive loads.

__________________
paulusgnome
Register to Reply Good Answer (Score 5)
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4
In reply to #3

Re: CAPACITOR CONNECTION TO VARIABLE-FREQUENCY DRIVE for Improving Power Factor.

04/06/2009 1:00 AM

This is absolutely correct. DO NOT connect any capacitors down stream of the VFD, it will destroy the VFD and the capacitors, plus it will have NO EFFECT on the power factor as seen by the utility source.

At the line input terminals, the VFD is already inherently correcting the displacement power factor, the kind the utility is concerned with, to around .95, so there is no justification for any additional improvement. The VFDs do increase the distortion power factor and if your utility mentions it, they may want that corrected as well, but most do not. To correct that, you need specifically tuned filters. Just adding capacitors on the line side of a VFD will set you up for resonance problems with the bus capacitors already in the VFD, and that can also lead to premature failure.

Use those capacitors somewhere else, but keep them away from the VFD.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Jul 2008
Location: UK
Posts: 205
Good Answers: 50
#6
In reply to #4

Re: CAPACITOR CONNECTION TO VARIABLE-FREQUENCY DRIVE for Improving Power Factor.

04/06/2009 5:30 PM

Yes, I agree wholeheartedly. Do not connect capacitors at the motor side of VFD. It will only cause 'Overcurrent' trip on the short circuit protection of the inverter output stage (doesn't harm VFD as protection is 'instant' and switches OFF all devices). There is also no need to fit Power Factor Correction capacitors at the power input as these are only fitted to improve on out of phase currents (improve displacement)

The capacitors in the DC link accept the reactive power drawn by the motor (lower pf) so this is the reason that Displacement Power Factor is near unity at the power supply side (normally 0.97+).

If you add reactors to the DC link (DCReactor) and/or the AC input this will dramatically reduce RMS input current improving the fundamental power factor, reamaining harmonics are more costly to correct by passive or active input filters, as you indicate. The DC choke is the most cost effective measure to improve RMS input current most effectively.

__________________
Something new every day!
Register to Reply
Associate

Join Date: Oct 2008
Posts: 39
Good Answers: 1
#5

Re: CAPACITOR CONNECTION TO VARIABLE-FREQUENCY DRIVE for Improving Power Factor.

04/06/2009 9:10 AM

Dear Friend,

Are these motors (5kW to 160kW and 375kW) connected in one (1) busbar as motor control center (MCC)?

If all these motors connected in one (1) busbar as MCC, then compute the total requirement of kVAR you need, then make or order one cubicle for your capacitor connected to the main busbar to compensate the whole motors' power factor.

Your power factor corrector (capacitor bank) should be self-healing type, complete with all protections and monitoring devices.

As other advices, never-never connect your capacitor downstream of vfd,

My above advice is being used for vfd with by-pass only. I'm sure it has a by-pass.

Eren

Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#7
In reply to #5

Re: CAPACITOR CONNECTION TO VARIABLE-FREQUENCY DRIVE for Improving Power Factor.

04/07/2009 1:15 AM

eren,

VFD with bypass??? Perhaps you are thinking of a soft start with bypass. Any bypass type of arrangement with a VFD would require break-before-make contacts and proper protection to ensure that the bypass and VFD are in phase with each other before operation. Furthermore, the sudden removal of the load from the VFD could damage the output section and leave a motor with a sudden and large mechanical and electrical shock-load. If there are such devices, I would like to know more.

--JMM

Register to Reply
Power-User

Join Date: Jul 2008
Location: UK
Posts: 205
Good Answers: 50
#8
In reply to #7

Re: CAPACITOR CONNECTION TO VARIABLE-FREQUENCY DRIVE for Improving Power Factor.

04/07/2009 3:43 AM

I work with inverters that have bypass prepared in control logic (just add contactors, sequencing done), in order to use VFD for starting and stopping the motor + Load.

Some inverters have output switching proof also to disconnect power with no damage. Reconnection entails matching the output to rotating motor speed or else plugging currents are demanded which cause tripping and potential damge to VFD. The removal of power usually has no impact on the motor but the reconnection could if done wrong.

If you have such applications and would like more information I could arrange to send or link.

__________________
Something new every day!
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#12
In reply to #8

Re: CAPACITOR CONNECTION TO VARIABLE-FREQUENCY DRIVE for Improving Power Factor.

11/21/2010 11:46 AM

Dear Mr. Malcolmk,

Thank you for your response and offering to send more link.

I am intrested to get more details from you and request you to send the links.

Thanks,

dhayanandhan.s

Register to Reply
Associate

Join Date: Oct 2008
Posts: 39
Good Answers: 1
#9
In reply to #7

Re: CAPACITOR CONNECTION TO VARIABLE-FREQUENCY DRIVE for Improving Power Factor.

04/07/2009 6:23 AM

To: Mr. jmueler,

Why? Have you not designed this for the large compressors and pumps? Try to ask Designer and Supplier like Siemens and Allen Bradley and others manufacturers of MV VFD,,, maybe you may add this to your experience.

Eren

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#11
In reply to #5

Re: CAPACITOR CONNECTION TO VARIABLE-FREQUENCY DRIVE for Improving Power Factor.

05/24/2009 3:05 AM

Dear Mr. EREN,

Thank you for your comments. All the drives which I have mentioned is in different locations and only 2 motors are in the same MCC. Hence, in my opinion, arriving at equivalent capacitors will not arise.

From this forum, I understand that capacitors should not be connected after VFD. My thinking is the motor winding heat while working is to be controlled, which may be due to less power factor as for as the motor is concerned.

I am extremly happy to see a large number of CR4 MEMBERS repliedFor my quiery.

THANKS TO CR4 FORUM ALSO.

DHAYANANDHAN.S,

INDIA.

Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#10

Re: CAPACITOR CONNECTION TO VARIABLE-FREQUENCY DRIVE for Improving Power Factor.

04/10/2009 10:00 AM

Thank you both MalcolmK and enereduarte. My experience, though significant, is obviously dated now. Good to hear of continuing developments in the field.

--JMM

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13

Re: CAPACITOR CONNECTION TO VARIABLE-FREQUENCY DRIVE for Improving Power Factor.

04/28/2020 7:34 AM

Power factor correction is usually done way upstream of any <...VARIABL FREQUENCY DRIVE...>, because its purpose is to better match the characteristics of the aggregated loads to the incoming supply and its feeder cables. The financial justification for doing it is based upon a penalty charge in the supply tariff. The technical reason for it is to make the supply cables run cooler by reducing the heating losses associated with current that is out-of-phase with the applied voltage.

Adding it downstream of a <...VARIABL FREQUENCY DRIVE...> is just plain nonsense.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#14
In reply to #13

Re: CAPACITOR CONNECTION TO VARIABLE-FREQUENCY DRIVE for Improving Power Factor.

04/29/2020 1:51 PM

If he did it 11years ago when this was posted, I'm sure he has suffered the consequences and learned his lesson by now...

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Register to Reply 14 comments