Can you retro fit an ac motor with a VFD or do you have to use a vfd compatible motor?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: VFD Motors

04/06/2009 11:14 AM

You can try but most of the time the insulation on the windings is not rated for the voltage levels that are seen using the VFD and the motor fails.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: VFD Motors

04/06/2009 11:21 AM

Yes in principle, provided it isn't a hazardous area motor located in a hazardous area. If this is actually the case then the installation needs to be fitted with a VFD and a replacement motor that have been tested and certified as a pair.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: VFD Motors

04/06/2009 4:11 PM

Motors that are designed for use behind VFDs offer distinct advantages over those that are not, but VFDs were actually designed to be used on any ac induction motor. The consequences of using a VFD on an older motor are totally dependent upon a number of variables;

  1. Voltage. If the line voltage is 380V or higher, a VFD rated motor provides extra protection from what are called "standing wave spikes" that can damage the insulation of older motors. 230V VFDs do not create the same level of peaks in the spikes and most motor winding insulation can handle them. If you want to use a 380V or higher existing motor on a VFD however, you can purchase retrofit load filters that will mitigate this problem.
  2. Operating speed. When you turn down the speed of the motor, you are also turning down the speed of the motor's cooling fan (if there is one) and thus reducing the amount of convection cooling it provided, So at very low speeds, the motor may end up burning itself up even though it is not over loaded. A standard motor is good for a turn-down ratio of maybe 4:1, whereas you can get VFD rated motors that are good to 1000:1. But if you are going to operate your motor at 50-75% speed, this is not likely to be an issue.
  3. Bearing damage. VFDs can cause a static charge to build up in the rotor and it discharges across the bearings and raced. The long term effect of this is that eventually the bearings and races become etched by a process similar to EDM (Electrical Discharge Machining) and fail prematurely. Good quality VFD rated motors will come with grounding bushings that provide a safe discharge path for the rotor currents. You can also buy retrofit grounding bushings for existing motors as well.

So the bottom line is, you CAN use non-VFD rated motors with VFDs, but you may have consequences. You can mitigate those consequences in existing motors, but on small ones, the costs may outweigh the cost of replacement. What I always tell people is to consider the application, installation AND the process costs. If having an inopportune motor failure while running is going to run the risk of significant product and/or production losses, spend the money for a VFD rated motor now. If not, run the one you have until it fails and replace it with a VFD rated one next time.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Good Answer (Score 2)
Anonymous Poster
#4
In reply to #3

Re: VFD Motors

04/07/2009 2:55 AM

Thanks for the info guys. What we are looking at is our pipeline pumps on an offshore production platform from the 80's which are running at a pressure that we have to reduce by appx 75% across our control valves which by adding VFD's we could save power. The pumps produce at 60 bar and the pipeline pressure is only 15 bar. I dont know why it was designed this way but a lot of over kill.

Reply
Active Contributor

Join Date: Sep 2008
Location: Rourkela,Orissa,India
Posts: 19
#5
In reply to #4

Re: VFD Motors

04/07/2009 3:13 AM

Hi guest,

Jref had given good comments on it.

Adding VFD will definitely save huge amount of power. Also, check whether pumps used are of overcapacity. Right size of motor selection would be more efficient.

Reply
Reply to Forum Thread 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); JRaef (1); PWSlack (1); spghadei (1); wareagle (1)

Previous in Forum: Sizing a Control Transformer for Various Loads   Next in Forum: Automatic Water Level Control Switch

Advertisement