Sensitive Earth Fault Protection

04/06/2009 10:50 PM

What are the required elements (CT /PT Requirements) to acheived sensitive earth fault protection in a general primary distrubution circuits?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Member

Join Date: Mar 2009
Posts: 9
Good Answers: 1
#1

Re: Sensitive Earth Fault Protection

04/08/2009 3:00 AM

CT (Current Transformer ) ratio is depends on rated full load current / control current. normally 5A for secondary.

PT (Potential Transformer ) ratio is depends on rated primary voltage / control voltage. normally 110V for secondary.

Accuracy class & VA Burden needs to be checked as per application.

Register to Reply
Anonymous Poster
#2
In reply to #1

Re: Sensitive Earth Fault Protection

04/08/2009 3:22 AM

Where can i accomidate (arrangement of IT's) CT & VTs to detect the fault in circuit?

Is 5P20 CT Core is enough to detect the fault / Class X core required?

Register to Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#3
In reply to #2

Re: Sensitive Earth Fault Protection

04/08/2009 7:20 AM

Dear,

At the input of the feeder terminal you can connect ct / pt .

5P10 / 5P15 would also be enough , but all that depends upon the fault levels.

What is the size of feeder ? rating of transformer ? length of feeder ?

__________________
Exploring the Science of Electricity
Register to Reply
Anonymous Poster
#4
In reply to #3

Re: Sensitive Earth Fault Protection

04/08/2009 7:26 AM

33 kV 2500A Feeder (600 mm width x 1200 mm depth X 2700 height)

X mer rating : 100 MVA

Length : form X mer is 5 meters

Register to Reply