Neutral Switch for Generators at Power Station

04/06/2009 8:50 PM

Dear all Electrical Gurus,

In one of my electrical power generation plant for glass container production ,i hv noticed there are 4 units of 640Kva DG in parallel (Sychronise) operation but only one of the neutral switch was in ON and three other unit were OFF position.

Please advise me why only one neutral switch need to ON not 4 units.

What is the correct method to switch on the neutral switches in the main switch board during the very begining to start the 1st DG , 2nd DG ,3rd DG and 4th DG. - All the time only one neutral switch need to ON ?

Thank you very much and Best Regards

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Active Contributor

Join Date: Feb 2009
Posts: 22
#1

Re: Generators Neutral switch

04/07/2009 6:02 AM

can you please explain your DG sets Synchronising procedure and Please attach scanned copy of your ckt diagram in your reply.Then we will get the answer.

Register to Reply
3
Power-User

Join Date: Oct 2008
Location: Jakarta Indonesia
Posts: 123
Good Answers: 7
#2

Re: Neutral Switch for Generators at Power Station

04/07/2009 10:19 PM

Dear all,

If there are more than one DG neutral is earthed,

1. 3rd harmonic current among DGs will increase. (If four DG has exactly same, this will not occur)

2. Circulating Neutral current among DGs will increase. (same as item 1)

3. Earth fault current increase.

(if one NER is 100A, four NER earthed = 400A earth fault current)

4. Earth fault protection become more difficult.

(One DG earth-fault may operate earth-fault relays of other DGs.)

Item 1 and 2 may not be a problem at all. Item 3 or 4 may be the reason why your DG plant has only one NER earthed.

Regards

__________________
Akihito Shigeno @ JGC-Indonesia
Register to Reply Good Answer (Score 3)
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#5
In reply to #2

Re: Neutral Switch for Generators at Power Station

04/08/2009 7:16 AM

Dear,

Very good reply .

Also, for stbility of parallel operation, The neutral of the master dg is switched on.( either manually switch or contactor ). All the fault currents shall pass thru only one neutral , protective instruments shall work more accurately.

Circulating currents in the neutral of dg sets shall be zero. So, stable neutral & zero voltage fluctuations & neusance trippings.

__________________
Exploring the Science of Electricity
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Mar 2009
Posts: 130
#7
In reply to #2

Re: Neutral Switch for Generators at Power Station

04/08/2009 9:47 PM

Dear Akihito Shigeno,

Thank you very much of your reply.

Regards

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#14
In reply to #2

Re: Neutral Switch for Generators at Power Station

03/15/2011 12:19 PM

Dear Mr.AkihitoShigeno,

During our college days our Professors taught in the class room, that the 3rd Hormonics is eliminated by Star Connection in the Alternator. 5th Hormonics reduced by short pitching of the windings.

Let the CR4 Forum members give their views or comment on 3rd Hormonics and "What are the standards adopted for 5th, 7th, 11th, 13th Hormonics and heat dissipation Standards on account of the above Hormonics."

DHAYANANDHAN.S

Register to Reply
Member

Join Date: Mar 2009
Posts: 9
Good Answers: 1
#3

Re: Neutral Switch for Generators at Power Station

04/08/2009 12:52 AM

Do you want to ask about neutral contactor????????

Register to Reply
Power-User

Join Date: Dec 2007
Location: Brasov, Romania
Posts: 255
Good Answers: 7
#4

Re: Neutral Switch for Generators at Power Station

04/08/2009 4:32 AM

Akihito Shigeno is somewhat right. But not only one neutral switch needs to be on.

The problem is given by the ground fault current value and also by the overvoltage value. By alowing a high ground fault current, there will be little concern with overvoltage, but the switching capacity needs to be taken in account. So the grouwnd fault current should not exceed the breaker rating.

On the other hand, if a ground fault occures and the current is low, the result is an overvoltage on the other 2 phases; this is bad for the phase-ground insulation for all the equipment connected in the network.

Engineers usually refer to the Xh/Xd ratio, where Xh is the homopolar reactance equivalent for a particular busbar or power line or DG, and Xd is the positive sequence reactance. Overall, the Xh/Xd ratio shoult be between 1≤Xh/Xd≤3.

1≤Xh/Xd is for the current on one phase ground fault should not be larger than Three phase -ground fault;

Xh/Xd≤3 stands for keeping the overvoltage not larger than 20% of rated voltage.

The Xh/Xd ratio can be modified by switching on/off the neutral switches. To determine how many switches need to be on/ off you have to do some calculation.

__________________
The time is ......now
Register to Reply Score 1 for Good Answer
6
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#6
In reply to #4

Re: Neutral Switch for Generators at Power Station

04/08/2009 9:09 PM

The answer given by Akihito Shigeno is pretty good. Let me explain it in another way.

The purpose of using NGR (Neutral Grounding Resistance) is to limit the earth fault current.

If the L-N voltage is VN and NGR value is RNGR.

Case 1 (One generator is grounded)

Assuming the fault resistance value 0, the earth fault current (IEF1) is

IEF1 = VN/RNGR

Case 2 (Two generators are grounded)

Between the line and neutral, there are 2 same NGR resistances are in parallel. The effective resistance of NGR is now half of RNGR (RNGR/2). So, the earth fault current (IEF2) is

IEF2 = (2xVN)/RNGR which is double of IEF1

Case 3 (Three generators are grounded)

Between the line and neutral, there are 3 same NGR resistances are in parallel. The effective resistance of NGR is now one third of RNGR (RNGR/3). So, the earth fault current (IEF3) is

IEF3 = (3xVN)/RNGR which is 3 times of IEF1

And so on …

So, to keep the same fault current for the system, only one generator is grounded at a time.

Hope it helps.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 6)
Power-User

Join Date: Mar 2009
Posts: 130
#8
In reply to #6

Re: Neutral Switch for Generators at Power Station

04/08/2009 9:48 PM

Dear msamad,

Thank you very much of your reply.

Best Regards

Register to Reply
Power-User

Join Date: Dec 2007
Location: Brasov, Romania
Posts: 255
Good Answers: 7
#10
In reply to #6

Re: Neutral Switch for Generators at Power Station

04/09/2009 3:56 AM

You're right. I wasn't paying attention at the voltage level. What i said is valid for high voltage, 110 kV and above. Below 35 kV usually the system is able to withstand a 40% overvoltage.

__________________
The time is ......now
Register to Reply
Power-User

Join Date: Mar 2009
Posts: 130
#9
In reply to #4

Re: Neutral Switch for Generators at Power Station

04/08/2009 9:50 PM

Dear nikolay,

Thank you very much

Regards

Register to Reply
Anonymous Poster
#11

Re: Neutral Switch for Generators at Power Station

04/09/2009 11:38 PM

Dear Aikhh,

For a solo single DG Alt with Y connection Neutral grounding is OK.

For a Multi DG in parallel, reason not to ground or make common connection for all DG Alternator s is to avoid the circulation current of 3 rd 5th, , , , harmonics generated in Alt Windings from One to Other winding. This causes overheating of winding and this circulating current is not noted in Amp meters. YHIS IS A VERY SERIOUS AND DANGEROUS PHENOMENON

I would advice you to open a chapter on Alternator or transformers running in parallel and STUDY Neutral grounding .. a book by M.G.Say.. etc. or any book on power station design.

Other opinions given by others are valid if you have DG at difft locations, but for one location multi DG one has to carefully do the job else a big difficult position may arise.

Best way u contact the agency, engineer who designed and gave instruction for the plant u have seen.

I wish U dont switch on 2 DG Neutrals simultaneously under any case Best Luck

Register to Reply
Power-User

Join Date: Mar 2009
Posts: 130
#12
In reply to #11

Re: Neutral Switch for Generators at Power Station

04/10/2009 5:55 AM

Dear Guest,

Thank you very much.

Register to Reply
Commentator
Engineering Fields - Electrical Engineering - New Member India - Member - New Member

Join Date: Dec 2009
Location: Bangalore,India
Posts: 80
Good Answers: 1
#13

Re: Neutral Switch for Generators at Power Station

02/09/2010 12:04 AM

Dear Forum members,

I have tried to understand the various explanations shared for the above question and i found it very informative. I had a doubt regarding the internal protection of alternator. I need to protect the stator windings against earth fault and if i have to use restricted earth fault relay and class-px CT to used in phases and neutral for sensing, then doesn't isolating neutral(either by switch or contactor) will cut off the sensing since the unbalance due to earth fault is sensed in the neutral. if restricted earth fault can't be considered in case of isolated neutral, what is the alternative for protection of stator windings?

Please state whether i a correct in the above doubt and kindly share your inputs.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#15

Re: Neutral Switch for Generators at Power Station

07/09/2024 10:44 AM

Please consult the Senior Electrical Engineer that wrote the procedure(s) in the first instance. That way a Mentor-Mentee relationship can be established, which will be valuable to all involved going forwards.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 15 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

aikhh (4); Akihito Shigeno (1); Anonymous Poster (1); dhayanandhan (1); harry potter (1); lavurk (1); msamad (1); nikolay (2); PWSlack (1); rajendra.kamble (1); shanbhag (1)

Previous in Forum: What's the Current at the Input for a UPS?   Next in Forum: Sensitive Earth Fault Protection
You might be interested in: Neutral Density Filters, Switch Boots

Advertisement