Anonymous Poster

over voltage alternator.

04/08/2009 2:13 AM

electrical guru..

how can i findout the maen cause of the over voltage of the alternator and how can i avoid this problem. because right now we suffering of alternator blowing in our substation project..

what protection i will fixed to protect my alternator during running of it..

best regard..more power....

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: over voltage alternator.

04/08/2009 2:59 AM

What does the manufacturer say on this topic?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster
#2

Re: over voltage alternator.

04/08/2009 5:07 AM

Firstly what is causing the alternator to go overvolts - usually this is due to bad setup of the governor failing to pull the energine speed back befor the overvoltage spike becomes an issue .

Rob

Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#3

Re: over voltage alternator.

04/08/2009 6:33 AM

dear,

did you tried for folowing checks...

1. Check for Capacitors... Over capacitors at the starting of DG may cause over voltages

2. Check for Over speed... Generally over speed protection is provided in AVR, does AVR have this feature ?

3. Check for performance of AVR, if you find the over voltages while in normal operating conditions , ( most of the time, at specific % of load say 25- 35 % rated load )other wise dg runs properly, then design of AVR is not good & calls for replacement of AVR by better quality AVR.

You may provide over voltage relay in the panel, to prevent high voltages being fed to the load.

__________________
Exploring the Science of Electricity
Reply
Member

Join Date: Mar 2009
Posts: 6
#6
In reply to #3

Re: over voltage alternator.

04/12/2009 1:29 AM

dear guru.

thank you for the information that you shared to me it helps a lot.

more power.

Reply
Active Contributor

Join Date: Mar 2009
Location: Abu Dhabi - UAE
Posts: 20
#4

Re: over voltage alternator.

04/08/2009 3:27 PM

You might need to check the following:-

1- Excitation field circuit (AVR - Automatic Voltage Regulator) of your alternator, as the higher the field the higher the output.

2- Check the speed governor of the prime mover for over speed control.

3- Check the magnetic pickup sensor for correct installation and healthy signal to the speed governor.(in case this is a Diesel engine set)

4- Check your overload setting of your main CB ( could be over rating ).

5- I f you have more than one alternator connected on parallel , make sure that they are synchronized and no reverse power is happening which make one of them act as a motor.

Hope that of help to you.

Salem

Reply
Member

Join Date: Mar 2009
Posts: 6
#5
In reply to #4

Re: over voltage alternator.

04/12/2009 1:25 AM

dear guru salem.

thank you for that information it helf a lot to me. the speed of the engene was accurate to 50hz and the voltage is 400v but after several minutes or sometimens a seconds only it wuold be goes to over voltage. and also when we connect to the grid the generator and the load is rise up to 2MW our generator was trip..

we have deisel generator substation it composed of 6 genset 500kva each. the capacity of substation is up to 3mw maximum and the demand is about 2.3mw or maximum.

about reverse current it has up in down its playing to 50-120kw its not fixed like i said it flactueting..

i hope your kindly response.

Reply Off Topic (Score 5)