Power Factor Correction

04/08/2009 12:01 AM

Could anyone supply me with info on how to calculate the average power factor, average power, KVA and KVAr and of a three phase system if a single phase power quality meter was used to measure the power and pf on all three phases, individually.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Dec 2006
Posts: 346
Good Answers: 6
#1

Re: Power Factor Correction

04/08/2009 12:56 AM

jorpaul; what kind of power quality meter do you have? 3 phase 3 wire 2 single phase meters, 3 phase 4 wire, 3 single phase meters required, perry

Register to Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#2

Re: Power Factor Correction

04/08/2009 12:58 AM

dEAR,

All being scalar parameters,

Average pf pf = (pf1 + pf2 + pf3 )/3

Total KW load = (kw1 + kw2 + kw3 )

Total KVAR = ( KVAR1 + KVAR2 + KVAR3 )

Total KWH = kwh1 + kwh2 + kwh3

__________________
Exploring the Science of Electricity
Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#5
In reply to #2

Re: Power Factor Correction

04/08/2009 4:35 AM

Thinking about it, assuming Vi and Ii being phase to neutral voltage(assuming Y connection) and line currents,

KW1 =V1I1CosΦ1

KW2 = V2I2CosΦ2

KW3 = V3I3CosΦ3

KW = KW1+KW2+KW3 =V1I1CosΦ1+V2I2CosΦ2+V3I3CosΦ3

In case of balanced then

KW = 3KWph = 3VphIphCosΦ

but it isn't is it ?

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Power Factor Correction

04/08/2009 3:00 AM

Ah! CR4's favourite topic: power factor.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Feb 2009
Posts: 22
#4

Re: Power Factor Correction

04/08/2009 3:31 AM

Now a days multi function meters are available in the market.you can connect to your supply .You will get result.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Oct 2008
Location: Jakarta Indonesia
Posts: 123
Good Answers: 7
#6

Re: Power Factor Correction

04/09/2009 2:03 AM

Dear all,

3phase power measurement by single phase power meter.

1 Connect volt probe to phase A and B

Connect amp probe to phase A.

Recored KW and KVar

2 Do not remove the volt probe at phase B, but move the volt probe at phase A to phase C.

Move the amp probe from phase A to phase C. Do not change the direction of Amp probe.

Recored KW and KVar

3 Total of both kW above is 3phase kW

Total of both KVar above is 3 phase kVar

3phase KVA is sqrt(sq(3phase kW)+sq(3phase kVar))

3phase PF is (3phase KW) / (3phase kVA)

Regards

__________________
Akihito Shigeno @ JGC-Indonesia
Register to Reply Score 1 for Good Answer
Anonymous Poster
#9
In reply to #6

Re: Power Factor Correction

04/26/2009 5:29 PM

Thank you, very profound.

Register to Reply
Anonymous Poster
#7

Re: Power Factor Correction

04/09/2009 4:42 PM

Power Factor (PF) is equal to the cosine of theta. Draw a right triangle with True Power (watts) on the base (side Adjacent) Reactive Power (VARS) on the vertical (side Opposite) and Apparent Power(KVA) on the hypotenuse. Use Trig to solve. The cosine of angle then should be expressed as Percentage and this is PF. A good PF for AC power is 95% (lagging- inductive) never go over 100% for utility supplied power, this would be leading (capacitive). So if reactive power goes up in relation to resistive power, then phase angle increase and PF decreases. So if angle theta is 25 degrees the Cosine is .9063 so the PF is 90.63%.

Register to Reply
Anonymous Poster
#8

Re: Power Factor Correction

04/26/2009 2:31 PM

P=VIcos phi,

where cos phi is the power factor

sohail

Register to Reply Off Topic (Score 5)
Register to Reply 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Akihito Shigeno (1); Anonymous Poster (3); harry potter (1); lavurk (1); perry (1); PWSlack (1); sb (1)