Hi i am using power cable 3C x 16sqmm + Eath, what is the appropriate earth cable size to be use. your help very much appreciate. Regard's.
Re: Cable sizing
04/20/2009 12:00 AM
Dear all,
If you do not care minimizing earthing conductor size, use 16 sq mm as PE, as per Table 54G, IEE (BS 7671).
Regards
Akihito Shigeno @ JGC-Indonesia
Re: Cable sizing
04/20/2009 2:13 AM
Usually, we will follows the power cable size. If you use 3C x 16sqmm then, the earth cable usually will be the same size of 16sqmm. Of course, you can also use one size down like 10sqmm for earth.
Re: Cable sizing
08/25/2011 6:12 AM
→ British Standard 7671.