We are having a ABB make VFD - ACS800 for fan application. It was commissioned and working for last three months. Now it is not responding to DCS input (4-20ma) and increse/decrese 24 V DC input from VFD panel for any increse/decrease command. Any change made from these two destinations leads to bringing the speed to ZERO with current indication in the existing value. However it is responding to HMI Keypad operation. No specific display in HMI screen. Kindly give your clarification to the above Mail Address.

Regards,

R.Thiyagarajn

Register to Reply
Pathfinder Tags: ABB VFD problem
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Active Contributor

Join Date: Sep 2007
Posts: 13
#1

Re: ABB VFD Problem

04/20/2009 2:14 AM

if it has communication pad/ cad change or check if iy somebody tampered with the control wiring.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: ABB VFD Problem

04/20/2009 3:29 AM

Also, get on the phone to ABB's technical helpline to see what assistance may be found there.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Sep 2008
Location: Rourkela,Orissa,India
Posts: 19
#3

Re: ABB VFD Problem

04/20/2009 3:34 AM

hi rajant,

i think the DCS input(4-20 mA) is for speed reference to the ACS800 VFD.

1. check the mA input from DCS at the VFD terminal.

2. whether it is connected to AI1 /AI2 / AI3.

3. Check the parameter 11.03 (If ur connection is at AI2 terminal, this parameter should be AI2)

4. u can check the actual signal of AI2 in the VFD keypad at parameter 01.19

if u are getting the actual signal okay, but ur drive is not responding, u can change the DCS input(4-20 mA) to the terminal AI3. Accordingly u have to change the parameter 11.03 to AI3.

Good Luck..