Exhuast fan and ducting sizing

04/20/2009 10:01 PM

Dear All Gurus,

I have a room size with 5mx5m and i need to install a exhaust fan with circular ducting which is lenght (install in vertical height) is 35m.

Please advise me how to size the following :

1.Exhaust fan capacity ( volume and Pressure)

2.Ducting size and exhaust air speed

Thank you very much

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Exhuast fan and ducting sizing

04/20/2009 11:48 PM

What type of room? What are you trying to exaust?

Where are you located? Do you have a mechanical/building code to follow?

Is there provision for make-up air? Or do you want a negative pressure room?

Register to Reply
Power-User

Join Date: Mar 2009
Posts: 130
#2
In reply to #1

Re: Exhuast fan and ducting sizing

04/21/2009 2:07 AM

Guest, thank you for your reply,

My is painting material store room in a manufactuere plant which is fully air conditioner (positive pressure),due some painting materials smell want to exhaust out.

Regards

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Exhuast fan and ducting sizing

04/21/2009 3:24 AM

It would be better to contain properly the materials that are causing the smell.

  • Are all the lids on?
  • What can be done to prevent spillages?
  • What operations can be moved into the fresh air?
  • What else is causing the smells?
  • Etc.

None of these are capital investments. They are basic housekeeping.

Why is the room air-conditioned if it is only a store room? If no-one works in there then could the air-con be turned off?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: Mar 2009
Posts: 2
#4
In reply to #2

Re: Exhuast fan and ducting sizing

04/21/2009 1:31 PM

Hi! hope you have how to size the fan already solved.

Will you send you "smell" out or scrubbe it? You, most probably, don´t want the smell to be transferred from your building to the community. Size of fan be influence by this fact too. vertical arrangement --if no scrubber-- is easy, use a double suction fan, bring downwards your cilindrical duct then divide it into two rectagular legs addressed to a top suction fan. Take care not to load the fan with the duct weight.

Regards & good look, WManso

Register to Reply
Guru
Engineering Fields - Environmental Engineering - New Member APIX Pilot Plant Design Project - Member - New Member

Join Date: May 2007
Location: Anywhere Emperor Palpatine assigns me
Posts: 2774
Good Answers: 101
#5

Re: Exhuast fan and ducting sizing

04/21/2009 10:55 PM

Volumetric flow rate (m3/min) = (volume of room x required no. of air changes/hr) ÷ 60. Pressure of 14.7 - 15psi is sufficient.

For 35 meter duct, air velocity of 40m/s is good. Duct cross-sectional area = air voulmetric flow rate (m3/sec) ÷ air velocity. From here you can work out the required duct Ø .

__________________
If only you knew the power of the Dark Side of the Force
Register to Reply
Anonymous Poster
#6
In reply to #5

Re: Exhuast fan and ducting sizing

04/22/2009 12:37 AM

on what data are these calculations made ? (40 m/s)

Because the units of Psi and m/s do not match.

Register to Reply
Power-User
United States - Member - New Member

Join Date: May 2008
Location: Arizona
Posts: 355
Good Answers: 4
#7
In reply to #5

Re: Exhuast fan and ducting sizing

04/22/2009 10:33 AM

Assuming a room height of 2.44m, gives a room volume of 61m^3; and volumetric change of 2 changes/h, produces 122m^3/h, or ~2m^3/min flow. A velocity of 183m/min puts me right in the middle of the chart, at about the 12.7cm (5 inch) dia duct, for a friction loss of 0.16"H20/30m (assuming I did all the metric-to-ft conversions correctly). I wonder if 2 changes/h would be enough to get rid of the smell.

Register to Reply
Power-User

Join Date: Mar 2009
Posts: 130
#8
In reply to #7

Re: Exhuast fan and ducting sizing

04/22/2009 7:57 PM

Dear flyinghigh,

Thank you very much of your very clear and good explaination to me.

Please advise what type chart you are usinf to calculate the air velocity ? and how to determine the suction blower pressure ?

Best Regards

Register to Reply
Power-User
United States - Member - New Member

Join Date: May 2008
Location: Arizona
Posts: 355
Good Answers: 4
#9
In reply to #8

Re: Exhuast fan and ducting sizing

04/23/2009 11:33 AM

Good morning, aikhh. I am using the Friction Loss in air ducts, Fig. 12-4, in "Air Conditioning and Refrigeration", by Jennings and Lewis, reproduced with permission from Heating Ventilating Air Conditioning Guide 1949. It plots cfm, fpm, in. duct diameter, and friction loss in inches H20/100ft.

If my calculations are correct, the blower pressure must be equal to the frictional loss of the entire length of duct, plus equivalent length of fittings, plus frictional loss of any filters or scrubbers, plus a safety factor. Good luck.