Induction Voltage

04/23/2009 11:12 AM

Hi guys,

We have laid a 16core, 8sqmm armoured power cable between panel and a centrifuge. Cable distance between them is about 100mt. We have only used 8 cores out of them. Now when panel is powered, we are seeing a voltage of 150volts in the spare unused core. Some suggested that it could be due to inductance. We checked cable insulation and continuity every looks fine. What could be the reason, because we cannot let the machine running with it armoured and Spare cable having voltage in it

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: Induction Voltage

04/23/2009 3:35 PM

Short answer is your likely getting magnetically induced voltages on the unused cores. Grounding the unused cores at one end (which you should have done in this application environment) should fix your problem.

__________________
jack of all trades
Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#2

Re: Induction Voltage

04/23/2009 10:23 PM

It is induced voltage all right- created due to mutual inductance between cables.

But makes me wonder . In balanced 3 phase lines this should have been cancelled off. 150V is a bit much, as you are obviously not using high voltage.

Why 8 cores being used?

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply
Power-User
United Kingdom - Member - New Member Engineering Fields - Transportation Engineering - New Member Technical Fields - Marketing/Advertising - New Member Hobbies - Target Shooting - New Member

Join Date: Sep 2007
Location: South coast of England
Posts: 411
Good Answers: 36
#3
In reply to #2

Re: Induction Voltage

04/24/2009 4:56 AM

The unused core will not couple equally to all the cores used for the 3 phase supply due to the different spacing between cores. It is highly unlikely that there will be complete cancellation. The unused core will become a current transformer which will generate a high voltage into a high impedance load.

Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#4
In reply to #3

Re: Induction Voltage

04/24/2009 7:02 AM

The difference in flux linkage will be minimal. And it will be more like voltage Transformer (1:1) ratio than CT. Also on this logic, if the armour is not earthed/ gets its earh disconnected, we should get a high voltage ?

Anyway 150V unbalance seems to be a bit high. Some thing seems to be not Ok. Is the load balanced ?

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply
3
Anonymous Poster
#5

Re: Induction Voltage

04/24/2009 10:21 AM

Why not just parallel up your unused conductors. At least it will reduce the resistance and you won't have them just floating. I would also suggest that you get the armor to a good ground.

Register to Reply Good Answer (Score 3)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#6
In reply to #5

Re: Induction Voltage

04/24/2009 10:27 AM

GA as yours was the best answer I read.

They should have laid two seperate cables, the problem would have been much reduced, if not completely fixed!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#7

Re: Induction Voltage

07/05/2009 4:19 AM

Mr.bmadhu

WHAT WAS THE NEED TO USE 16 CORE CABLE WHEN 8 CORE ALONE IS USED.?

You have mentioned only the distance between the machine and board. what was the cable length used.? If it is more than the required if it is coiled to adjust the length, then the induction and hence the problem starts.

Sorry for the delay in interacting.

DHAYANANDHAN.S

Register to Reply
Commentator

Join Date: Nov 2007
Posts: 86
#8
In reply to #7

Re: Induction Voltage

07/05/2009 11:20 AM

Hello every one,

This all started, because we had no proper drawing at the time of cabling and it was urgent.We had to lay it based on other centrifuge drawing. Later only 8 cores were used. Since this one was a old one with not many interlocks.It connects two panels through a cable tray and no cable is looped in between. and to my surprise it has glands on both ends both of them are earthed, still we have voltage on unused cores

Register to Reply
Register to Reply 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Andy Germany (1); bmadhu_srao (1); Chankley (1); dhayanandhan (1); jack of all trades (1); sb (2)

Previous in Forum: Vid for PWSlack & all you Steam Enthusiasts   Next in Forum: AC and eddy.
You might be interested in: Cable Laying Services, Cable Assemblies, Cable Trays

Advertisement