Energy cost reduction for HVAC on a production floor

04/23/2009 7:29 PM

I work in a plastics compression molding facility. The process runs around 400 deg. F. give or take. The current philosophy here is to use exhaust/ intake hoods over the extruder barrels and use air handlers to cool the inside air. The way I see it is: we are wasting energy trying to cool heated ambient air. This actually only accounts for approx 60% of the heat generated. The rest comes from the associated electrical apparatus and the product itself.

I have tried for 3 years to convince the leadership that it would be more efficient and cost effective to exhaust the hot air through the roof with thermostatically actuated vents to no avail.

Does anyone know how I can calculate the ROI on something like this?

The production area is roughly 300' x 200' withe 23 pieces of equip generating 400+ degrees F. and associated motors and electrical controls. there are 8 large air handlers cooling the ambient air. In the summer average ambient temp. is 90- 95+ F.

Thanks

__________________
Tell 'em what they need to hear; not what they want to hear!
Register to Reply
Pathfinder Tags: energy conservation ROI
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#1

Re: Energy cost reduction for HVAC on a production floor

04/24/2009 9:19 AM

If the ambient air is above the average outside air temperature (not just in the summer), then it would save energy to use 100% outside air.

One nice thing about that is that the cooled air supply can be directed at operators' spaces, much like "spot coolers."

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply
Power-User

Join Date: Jun 2006
Location: Manila Philippines
Posts: 171
Good Answers: 8
#2

Re: Energy cost reduction for HVAC on a production floor

04/25/2009 2:55 AM

Hi Noshort,

First nice to hear that you have concerned on company regarding energy conservation. However, for 3 years now they don't bother and listen on you. I would say due to lack of proper presentation, support and justification where ROI is one of the great issue during the presentation/discussion stage.

As your question: "how to calculate the ROI"? my simple idea is.

Target Savings in terms of $$$$$ - cost of investment = ROI.

Taking into accounts, the objective mustn't adversely affect the operation and or sacrificing the health condition of the staff as maybe the management also thinking staff working environment as they also includes on thier computation how much it cost for future staff hospitalization? but i would say your idea is very great! keep on trying. if you can save 30% on energy cost or maybe more, don't give up. This is my 4th year now of waiting for my Building Energy Management computerization system, which is budgeted approved however lack of funding then maybe we have the same problem, for sure the management did not forget or ignore your proposal however it could be lack of actual funding.

Also good luck!!!!

Kind regards

Roman

Register to Reply
Power-User
United States - Member - US Navy Veteran

Join Date: Mar 2007
Location: Nothing sucks more than that moment during an argument when you realize you're wrong.
Posts: 301
Good Answers: 22
#8
In reply to #2

Re: Energy cost reduction for HVAC on a production floor

04/26/2009 9:30 AM

"I would say due to lack of proper presentation"

That was what I eventually figured out when back I did projects. I tried telling them (management/accounting) what made sense to me, but it was like I was talking to my sisters children. Through careful listening and observing I figured out "what they wanted to hear" and geared my presentations toward that, explaining to the contractors, consultants and vendors that when the conference room door closed , I was representing their product or idea....not them. I turned into a salesman during the meetings and learned how to get things done. CAUTION!...do not lie...you loose all trust and credibility..there are many buzz words/ phrases at your disposal but only use the ones they want to hear.

This is all assuming that it's a legit project that should be done in the first place.

__________________
You never know when it will strike, but there comes a moment when you know that you just aren't going to do anything productive for the rest of the day.
Register to Reply
Member

Join Date: Apr 2009
Location: Philadelphia, Pennsylvania, USA
Posts: 9
Good Answers: 1
#3

Re: Energy cost reduction for HVAC on a production floor

04/25/2009 6:11 AM

Your idea is a good one. However, management will only be intereted if you present to them in such a way that they will improve thier bottomline. Present a positive ROI is the way to go. It's not that difficult to do, however, we need more information. That's the difficult part. You need to do some homework. Here's what you need:

What it would cost to run the new equipment (monthly) - The cost to run the current equipment (Monthly) = Net monthly savings.

Then, get your total cost of the new equipment installed and divide that by the Net MonthlySavings = Your Breakeven Point (BEP) in months.

Then you can determine your ROI by taking 12 months divided by your BEP = ROI%

Example: Let's say the existing equipment costs $2400 per month to run and the new equipment will cost $1400 per month to run. That means your Net Monthly savings is $1,000 per month.

We'll estimate the cost of the new equipment at $36,000 divided by your Net Monthly Savings of $1,000 per month = a 36 month BEP.

Then take 12 months divided by your BEP of 36 months = An ROI of 33.3%

Then take that to management and ask them where they can invest their money anywhere today and get that kind of Return on Investment?

They'll be alot more interested in hearing what you have to say.

__________________
"How many legs does a dog have if you call the tail a leg? Four. Calling a tail a leg doesn't make it a leg ." - Abraham Lincoln
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Nov 2008
Posts: 158
Good Answers: 1
#4

Re: Energy cost reduction for HVAC on a production floor

04/25/2009 9:09 AM

1. Calculate the total heat load

2. Get a firm figure on an induction hood TOTAL installed cost. This brings in fresh air in front of the apparatus and pulls exhaust from the rear. This has 2 benefits: you will only remove about 5% of the conditioned building air, while exhausting the hot air and (2) it creates an air curtain effect.

3. Estimate the a/c energy used to bring the heat load down to building ambient.

4. Add together the #2 cost plus the energy to run it.

5. Subtract this from #3. This is your ROI (less the 5% of course).

We do this type of work on a regular basis and successfully sell the total package based on ROI.

Register to Reply
Power-User

Join Date: Jun 2008
Location: Olive Branch, Ms. USA
Posts: 124
#10
In reply to #4

Re: Energy cost reduction for HVAC on a production floor

04/27/2009 7:02 PM

There are hoods installed lineraly over the extruder barrells. The problem is that the same hood brings in fresh outside air and exhausts the heat with no division of space.

__________________
Tell 'em what they need to hear; not what they want to hear!
Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#5

Re: Energy cost reduction for HVAC on a production floor

04/25/2009 9:21 AM

Noshorts,

As Peteciliberto has said, run the numbers to see if your ideas are sellable. Many companies will not look at any capital expenditures if the ROI is any less than 33% (or some other number close to this).

It is also possible that your approach is trying to answer the wrong question(s).

  • In the commercial kitchen industry as well as in fireplace technology, the best energy savings with air exhaust problems are to bring in fresh air without conditioning it, directly from the outside, to replace 100% of the air being exhausted. This is done in such a way that the air intake is minimally mixed with the building's ambient air. Thus, the cost of conditioning the ambient air is minimized because the makeup process air is separated from it. I'm not sure if your description of the company's current process is what I have described above.
  • Have you looked at reducing the heat loss from the process equipment? Better insulation of this equipment may be possible, leading to a reduced operating cost per unit produced. The side benefit is decreased need for conditioning the ambient air and increased worker comfort and safety. Poor insulation is often a result of aging, wear & tear, maintenance practices, and equipment design obsolescence.
  • What about the cooling of the product itself? You indicate that it is a source of heat within the factory. Can fan-directed air flow be designed to exhaust some of this waste heat in a way similar to that for the equipment?
  • Is it possible to use any of the "waste" heat via heat exchange or heat recovery systems, to supply a portion of the heating energy needs of the plant? This is a change in perspective--instead of seeing the heat as a waste product to be thrown away it is seen as a resource to be utilized or sold.

Let us know your opinions on these things. --JMM

Register to Reply
Participant

Join Date: Feb 2008
Posts: 3
#6

Re: Energy cost reduction for HVAC on a production floor

04/25/2009 12:01 PM

Not knowing your process, is there something else that you can do with this waste 400 degree energy instead of blowing it into the atmosphere? Check out www.sidelsystems.com

Register to Reply
Power-User

Join Date: Apr 2007
Location: New york
Posts: 139
Good Answers: 6
#7

Re: Energy cost reduction for HVAC on a production floor

04/25/2009 2:36 PM

Can you utilize the hot exhaust to generate power ?

__________________
In such a vast universe, I can only bask in my own insignificance....
Register to Reply Score 1 for Good Answer
Anonymous Poster
#9

Re: Energy cost reduction for HVAC on a production floor

04/26/2009 11:56 PM

if you want a solution you can contact pawan@mechartes.com +919811408957 this an IIT based engineering services company they will solve the problem by using CFD .

gagan

Register to Reply
Active Contributor

Join Date: Aug 2006
Posts: 18
#11

Re: Energy cost reduction for HVAC on a production floor

04/28/2009 10:00 PM

Noshorts

Here's an outside the box idea to chew on. Check out heat pipe technology, understand how it works and see if you can make it work to syphon the heat off your presses. No moving parts, lot cheaper to operate, quick payback. I use these as cabinet coolers(Noren) in my very dusty environment, no problems since installation.

__________________
John 3:16
Register to Reply
Register to Reply 11 comments

"Almost" Good Answers: