Hardness of Boiler Blowdown Water

04/27/2009 3:16 AM

Hello Everybody,

Here I have doubt on the boiler blow down water. We are maintaining only TDS , PH & Sulphides of Boiler blow down water. my doubt is what should be the Hardness of Blowdown Water, generaly we are not measuring it only we maintening the Feed water Hardness below 2ppm, we are having softner not DM plant.

Pl guide me

JORAVI

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Boiler Water

04/27/2009 3:53 AM

What is the boiler operating pressure?

  • For a low-pressure boiler (<15barg), a blowdown TDS of 2000-2500 is not uncommon, and 3000 might be on the upper end of tolerability.

What does the boiler manufacturer recommend?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Apr 2009
Posts: 20
#2
In reply to #1

Re: Boiler Water

04/27/2009 7:43 AM

Hello, Thanks. Boiler operating pressure is 10.5 bar and generation is 6MT/Hr, I am interested in knowing the hardness of blow down water not TDS . Feed Water hardness is 1ppm. Pl give your feedback. joravi

Register to Reply
Power-User

Join Date: Sep 2007
Location: I am located in Mumbai,India.
Posts: 125
Good Answers: 2
#3
In reply to #2

Re: Boiler Water

04/28/2009 2:01 AM

Blow down water hardness is same as TDS in boiler since you are removing water from boiler. The TDS should not cross 3000ppm. You should adjust blowdown accordingly

__________________
Rajesh
Register to Reply
Commentator

Join Date: Dec 2008
Location: Young NSW Aust
Posts: 81
#4
In reply to #3

Re: Boiler Water

04/28/2009 2:55 AM

You can maintain a higher TDS depending on your caustic alkalinity. A lot depends on what type of hardness you have in the Boiler. If you have a fairly high silica level then you will need to adjust your alkalinity.

This is a guide only, there are lots of variables. You need to test your water for nasties before making any decisions.

Register to Reply
Anonymous Poster
#6
In reply to #4

Re: Boiler Water

04/28/2009 8:11 AM

We are maintaining Boiler Water TDS below 3000ppm, here my doubt is, if we measure the hardness of that blowdown water then what will be approximate range that measurement. for Example Feed water hardness is 1ppm and Feed water TDS is 20ppm Boiler Blow Down water TDS<2800 , Boiler Blow down hardness= ? Steam generation rate =6MT/Hr at pressure 10.5Kg/Cm2

Register to Reply
Power-User

Join Date: Oct 2007
Location: NW Ohio
Posts: 411
Good Answers: 25
#5

Re: Hardness of Boiler Blowdown Water

04/28/2009 8:06 AM

We also need to know if you are getting a large percentage of return condensate and if your demand is steady or in large gulps? How is your surface blowdown set up?

__________________
Goodness has nothing to do with it.
Register to Reply
Active Contributor

Join Date: Apr 2009
Posts: 20
#7
In reply to #5

Re: Hardness of Boiler Blowdown Water

04/28/2009 8:15 AM

We are maintaining Boiler Water TDS below 3000ppm, here my doubt is, if we measure the hardness of that blowdown water then what will be approximate range that measurement. for Example Feed water hardness is 1ppm and Feed water TDS is 20ppm Boiler Blow Down water TDS<2800 , Boiler Blow down hardness= ? Steam generation rate =6MT/Hr at pressure 10.5Kg/Cm2

Register to Reply
Guru

Join Date: Feb 2009
Location: Tamilnadu, India
Posts: 836
Good Answers: 42
#8

Re: Hardness of Boiler Blowdown Water

04/28/2009 10:39 AM

The blow down water characteristics are likely to be closer to boiler in feed water.Whereas in feed water conditions are to be monitered as per needs,is there any specific condition to moniter blow down water parameters?

__________________
Nature is so graceful and naked. Human possession is ridiculous.
Register to Reply
Power-User

Join Date: Oct 2007
Location: NW Ohio
Posts: 411
Good Answers: 25
#9

Re: Hardness of Boiler Blowdown Water

04/28/2009 11:08 AM

If you are keeping the boiler TDS at 3000 you may be giving away a lot of BTUs. The main reason for keeping the TDS low is to prevent carry over. You can save fuel costs if you run TDS up to 4500 or even 5000.

If you can monitor your steam quality closely you need to raise the TDS until you find out when carryover takes place and adjust your TDS back down from there.

It doesn't sound like hardness is something to worry about because it is so low at the feed water tank. Consult with your water treatment guys.

__________________
Goodness has nothing to do with it.
Register to Reply
Active Contributor

Join Date: Apr 2009
Posts: 20
#10
In reply to #9

Re: Hardness of Boiler Blowdown Water

04/29/2009 5:41 AM

We are maintaining TDS below 3000ppm only to keep the boiler water tubes in healthy condition & to get maximum life of the Boiler tubes.

As a curiosity, I have measured Hardness of blowdown water, it is coming 20ppm.

Now I am intersted to know whether this data is acceptable or not.

Register to Reply
Power-User

Join Date: Oct 2007
Location: NW Ohio
Posts: 411
Good Answers: 25
#11

Re: Hardness of Boiler Blowdown Water

04/29/2009 8:03 AM

20PPM hardness is fine. However, why are you so determined to avoid hardness at the expense of everything else?

Hardness is only one consideration when operating your system.You may be paying more in excess fuel costs trying to avoid hardness than is really necessary.

__________________
Goodness has nothing to do with it.
Register to Reply
Active Contributor

Join Date: Apr 2009
Posts: 20
#12
In reply to #11

Re: Hardness of Boiler Blowdown Water

04/29/2009 8:15 AM

Thanks Mr Beriberi, Ok now my doubt is cleared. I was thinking that ,as all hardness we are removing in softener, Boiler blowdown water hardness will be same as feedwater hardness. I was wrong. Thanks to all who participated in discussion in my apprehensiveness.

Register to Reply
Register to Reply 12 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); beriberi (3); joravi1 (4); PWSlack (1); rsalaskar (1); s.udhayamarthandan (1); whezmabeer (1)

Previous in Forum: Speed Governor for Steam Turbine   Next in Forum: Are Split Air Conditioners Harmful to Human Health?
You might be interested in: Boiler Services, Boiler Controllers, Hardness Testers

Advertisement