Differential Pressure Transmitters

04/27/2009 7:52 AM

dear sir,

i used yokogawa EJA10 dp transmitter for steam flow measurement . my calibration range is 0-2500mmwc. the problem i face that after reaching 86% dp automatically go to zero . i check dp transmitter calibrate it . it is working ok. can anybody help me how this problem occur. steam flow range is 0-16 TPH. lilne size : 100 mm

orifice dia : 61mm.

temp 130 deg.c

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator
India - Member - Naveen Menon Engineering Fields - Instrumentation Engineering - Naveen Menon

Join Date: Oct 2007
Location: India
Posts: 92
Good Answers: 2
#1

Re: dp transmitter

04/27/2009 7:59 AM

Few questions

From where is the tapping taken. Top of the pipe or bottom?

Does it happen everysingle time it crosses 86%.

Where have you seen zero in TX or in The HMI or PLC. Did you see what is the mA at 85% in the TX and what is it at 86%.

i belive the URV equal to 20 mA and configured correctly as 100% in HMI & PLC.

Register to Reply
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#2

Re: dp transmitter

04/27/2009 9:08 AM

Please clarify.

86% of what? of 2,500? Do you mean that when the differential pressure reaches 2,150mmWC, the transmitter output goes to 0mA or 0mmWC?

With insufficient information, I'll have to make a guess. I think you may be be dealing with the "burnout" parameter ('don't know what yokogawa calls it). That's a parameter that some transmitters have to set the output at some value (usually either 0 or 100% - 4 or 20mA) when the measurement goes above a certain value. It's used for fail-safe purposes.

I usually see the burnout parameter with temperature transmitters but other transmitter types also have them.

regards,

Vulcan

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply
Commentator
India - Member - Naveen Menon Engineering Fields - Instrumentation Engineering - Naveen Menon

Join Date: Oct 2007
Location: India
Posts: 92
Good Answers: 2
#4
In reply to #2

Re: dp transmitter

04/28/2009 1:35 AM

HI Vulcan

I dont think thats likely because he's calibrating it full range, found ok. Also this happens everytime as per his explanation,. Could be the temp sensor in the Tx that could do this. Also from his explanation seems this Dp tx is for flow. so may be wrong config in the HMI or PLC also could create the problem.

But he needs to explain 86% of what first.

Register to Reply
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#5
In reply to #4

Re: dp transmitter

04/28/2009 8:46 AM

But he needs to explain 86% of what first

Which is why I said I'd make a guess. Also, it wasn't clear enough to me that he had calibrated it to full range. I interpreted his statement that when he reaches 86% applied pressure, the display suddenly goes to zero. That sounds very much like a burn-out parameter kicking in.

If he can come up with a more complete description, we can give a better answer.

regards,

Vulcan

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply
Active Contributor

Join Date: Feb 2009
Location: india
Posts: 12
#6
In reply to #2

Re: dp transmitter

04/29/2009 4:25 AM

Thank for interesting in my question.

first i calibrate dp transmitter with help of comarision tester. i check with apply 2100mmwc,2200mmwc and 2500mmwc pressure to transmitter. as per pressure output of mA are correct. dp give output upto110% (in display)

i fixed this transmitter with my orifice. i take orifce tapping 45 degree from top of taping and through condensate port.

we measure steam consumption through this flow meter.

it is working first class up to 85% of our calibration range. but when dp shows above 85.2% in display after then it is directly show "0". i check mA it is 3.97 mA.

thanks with regards

hitesh purani

Register to Reply
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#8
In reply to #6

Re: dp transmitter

04/29/2009 10:44 AM

What is the transmitter brand and model number?

Also, steam taps go to the side of the orifice flange, not 45° from the top. Do you have enough length in your impulse piping to prevent live steam from getting to your transmitter? You didn't mention how you connected it but just in case, I'm putting a drawing from Rosemount's 1151 manual.

regards,

Vulcan

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply
Anonymous Poster
#3

Re: Differential Pressure Transmitters

04/27/2009 11:26 AM

Do the transmitter specifications allow the unit to be used with steam? Usually that is too hot for a pressure transmitter and it will act funny.

Register to Reply
Active Contributor

Join Date: Feb 2009
Location: india
Posts: 12
#7
In reply to #3

Re: Differential Pressure Transmitters

04/29/2009 7:18 AM

sir i used yokogawa EJA10 dp transmitter.

as per datasheet the temp range is 80 degree. we not apply steam directly.

we use condesate pot for steam application. temp range of steam is 135-145 deg. c.

thanks

hitesh

Register to Reply
Commentator
India - Member - ADIL MOULA Engineering Fields - Instrumentation Engineering - Adil Moula

Join Date: Jun 2008
Location: India
Posts: 95
Good Answers: 1
#9
In reply to #7

Re: Differential Pressure Transmitters

04/30/2009 3:32 PM

hi

I had many doubt how is the

1 orifice installation vertical or horizontal.

2 direction of orifice is with the impulse tapping ie inlet of orifice should be the hp tapp and with the direction of flow

3 condensate pots leveled equally or there any offset between them .

4 check for equalising valve fully close

this should solve your problem if not give the feedback

Register to Reply