RTDs and Incorrect Temperatures

04/28/2009 7:49 AM

if RTD (pt 100) gives some resistance,then as per resistance its temp.indicator not show the correct temp.it indicate 8 to 10 C lower then as per RTD resistance.

we calibrate the Temp indicator it was perfectly ok.its power supply is 230 VAC.

RTD was also ok, three wire

Cable was also ok so what is the reason for this type of error.can you guide me !!!!

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Jul 2007
Location: The cigarette-stained drunkard living in the cardboard box outside Marks & Sparks delivery entrance, Eastgate Shopping Centre, Basildon.
Posts: 487
#1

Re: Temp indicator

04/28/2009 8:05 AM

Guvnor - are the lead resistances correct?<Splutter>

__________________
Essex jobs for Essex yobs! <Burp>.
Register to Reply
Active Contributor

Join Date: Nov 2008
Posts: 10
#2
In reply to #1

Re: Temp indicator

04/28/2009 8:08 AM

yes,

Register to Reply
Power-User

Join Date: Jul 2007
Location: The cigarette-stained drunkard living in the cardboard box outside Marks & Sparks delivery entrance, Eastgate Shopping Centre, Basildon.
Posts: 487
#3
In reply to #2

Re: Temp indicator

04/28/2009 8:10 AM

And does it correspond with the standard PT100 RTD temperature/resistance table? <Cough, wheeze>

__________________
Essex jobs for Essex yobs! <Burp>.
Register to Reply
Power-User

Join Date: Jul 2007
Location: The cigarette-stained drunkard living in the cardboard box outside Marks & Sparks delivery entrance, Eastgate Shopping Centre, Basildon.
Posts: 487
#4
In reply to #3

Re: Temp indicator

04/28/2009 8:32 AM

If it doesn't, then it's fu broken and you need to change it. <Cough>

__________________
Essex jobs for Essex yobs! <Burp>.
Register to Reply
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#5
In reply to #4

Re: Temp indicator

04/28/2009 9:49 AM

Hi Pete,

It doesn't sound logical. If:

  • the temperature indicator is calibrated properly
  • the RTD checks out as okay and
  • the wires are all the same resistance

it should work okay. If it doesn't, one or more of the above is incorrect.

regards,

Vulcan

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply
Anonymous Poster
#6

Re: RTDs and Incorrect Temperatures

04/28/2009 2:36 PM

The readout and the probe should be aligned at a known value. Usually ice point. This will align the probe to the readout and if all else is linear and cal'd correctly should correct for any error in the system.

Register to Reply
Power-User
New Zealand - Member - Member Australia - Member - Member

Join Date: Oct 2008
Location: Auckland, New Zealand
Posts: 463
Good Answers: 43
#7

Re: RTDs and Incorrect Temperatures

04/29/2009 12:13 AM

Some indicators can have an offset which can cause some brain strain.

What is the resistance value for your RTD and what is the indication of your meter at the same conditions.

Are you able to put a known value resistor to the indicator input and read the value?

Register to Reply
Commentator
India - Member - Naveen Menon Engineering Fields - Instrumentation Engineering - Naveen Menon

Join Date: Oct 2007
Location: India
Posts: 92
Good Answers: 2
#8

Re: RTDs and Incorrect Temperatures

04/29/2009 12:55 AM

I did see a similar instance once. I removed the RTD wire at the TB in the JB between RTD and Panel and cleaned the TB, cleaned the lead of the wires and put it back and the 10 dc difference was gone.

You could try though

Regards

Naveen

Register to Reply
Power-User
South Africa - Member -

Join Date: Nov 2008
Location: Johannesburg
Posts: 295
Good Answers: 12
#9

Re: RTDs and Incorrect Temperatures

04/29/2009 1:42 AM

Hi all,

Firstly - Temperature measurement with RTD or Thermocouple is definately not linear.

Now to the problem.

Measurement circuits that accept three-wire inputs minimize the effects of lead wire resistance as long as the outer legs are equal. However factors such as terminal corrosion and loose connections can still create sinificant differences between the lead resistances seen by the measurement circuit, because only one ohm of difference between the legs results in an error of 4.7 deg F (2,6 deg C).

So this should give you your starting point - lead wire lengths, loose connections, corroded terminals. I suspect it would be one or more of the above mentioned if your element is 100% as well as the transmitter.

Regards

Craig

Register to Reply
Commentator

Join Date: Oct 2007
Location: Caribbean
Posts: 79
Good Answers: 2
#10

Re: RTDs and Incorrect Temperatures

04/29/2009 9:27 AM

When calibrating , do you have the RD hooked up to the final display or are you just reading resistance with a multimeter in the shop and comparing to the RTD resistance/temperature chart.

RTDs work by having a constant current source pass through the RTD.

Measure the loop current on this defective circuit and compare to a known good circuit.

Maybe you cc source is a bit low

__________________
Learn more, Do more , Be more
Register to Reply
Anonymous Poster
#11

Re: RTDs and Incorrect Temperatures

04/29/2009 10:26 AM

Some indicators use a 24 V DC supply. If this voltage is incorrect then you may face such problems

Register to Reply
Anonymous Poster
#12

Re: RTDs and Incorrect Temperatures

04/29/2009 3:43 PM

Is the rtd in a well or in direct contact with the process?If in a well, do you use a thermal compound between the rtd and the well bore?If in a well, is the external portion of the well clean and free of debri?Are connections tight and clean?(both ends).There are 2 curves for RTD's. Both are 100 ohm at 32 degrees, but the response is different. Are you sure you have the right curve?

--------------SSB-----------------------------------------------------

Register to Reply
Commentator
India - Member - ADIL MOULA Engineering Fields - Instrumentation Engineering - Adil Moula

Join Date: Jun 2008
Location: India
Posts: 95
Good Answers: 1
#13

Re: RTDs and Incorrect Temperatures

04/29/2009 4:23 PM

hi harsh check with rtd simulator from rtd point to controller ie ; remove 3 wire from the rtd and in place of rtd connect simulator or decade box and feed the resistance as per the resistance chart if the error persist check the lead contacts in junction box or any unbalance lead resistance . www.telcoenvirotrols.com/ACI_100_ohm_resistance_chart.pdf hope u will resolve it

Register to Reply
Participant

Join Date: Jan 2009
Posts: 4
#14

Re: RTDs and Incorrect Temperatures

04/30/2009 3:24 PM

hi dear ,

set the tempture controller off set parameter ,then see what happened.

__________________
SANO
Register to Reply
Commentator
India - Member - ADIL MOULA Engineering Fields - Instrumentation Engineering - Adil Moula

Join Date: Jun 2008
Location: India
Posts: 95
Good Answers: 1
#15
In reply to #14

Re: RTDs and Incorrect Temperatures

04/30/2009 3:39 PM

how much to set the offset 8deg or 10 deg

Register to Reply
Anonymous Poster
#16
In reply to #15

Re: RTDs and Incorrect Temperatures

05/07/2009 1:34 PM

HI DEAR ,

you send me temperature controller type , model no , company name , then i tell you how you set off set parameter.

Register to Reply