Sun Shade Protection

04/28/2009 1:30 PM

Hello Frnds

Ther are these Client standards mentioning the requirement for Sunshade Protection for Local Instruments (Tranmitters)

If the instrument is rated is rated for IP 66 , Nema 4X, Can i Bypass these shelters??

Regards

Jose John

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Aug 2007
Location: Earth - I think.
Posts: 2143
Good Answers: 165
#1

Re: Sun Shade Protection

04/28/2009 2:10 PM

No.

The IP and NEMA ratings don't spec or protect against the radiant heat from the sun.

You don't say where this project is located. I work in the desert where temperatures can get to 125 Deg F (in the shade!). If the cabinet holding my PLCs and instrumentation aren't shaded, I have seen it reach 160 Deg F inside the enclosure. Not good, since the PLCs and radio modems die at 140 Deg F.

A sunshade is a lot cheaper than $10K-$20K of fried electronics.

__________________
TANSTAAFL (If you don't know what that means, Google it - yourself)
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: Sun Shade Protection

04/28/2009 3:23 PM

If the instrument is rated is rated for IP 66 , Nema 4X, Can i Bypass these shelters??

No, that's like standing outside in the hot sun with a raincoat on. No protection.

Bear in mind that a sun shade doesn't necessary mean an enclosed shelter surrounding the enclosure being protected, it can consist of as little as a sheet of steel supported on an angle above the enclosure to block the sun (depending on the situation).

__________________
jack of all trades
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Sun Shade Protection

04/28/2009 7:20 PM

Can i Bypass these shelters??

NO!

Register to Reply
Commentator
India - Member - Naveen Menon Engineering Fields - Instrumentation Engineering - Naveen Menon

Join Date: Oct 2007
Location: India
Posts: 92
Good Answers: 2
#4

Re: Sun Shade Protection

04/29/2009 1:09 AM

when you say local instruments does that include only transmitters/ guages etc or does it also include PLC's etc.

For guages and others in same category no Sunshade required.

For plc's - alwyas better to have enclosures which are temperature controlled.

For transmitters it is better to have sunshades mate. Ussually good tx like Rosemount provide good lperformance even in ambient from -40 to 85 dc.

Register to Reply
Power-User
South Africa - Member -

Join Date: Nov 2008
Location: Johannesburg
Posts: 295
Good Answers: 12
#5

Re: Sun Shade Protection

04/29/2009 1:32 AM

Hi all,

Sunshade is ok. The real problem is UV (Ultra violet) protection for the casing. The other problem would be solar radiation (temperature effect).

The IP/NEMA rating is only for ingress protection - not UV or temperature.

If the ambient temperature is very hot - you will have to use either sun shade or some sort of enclosure with purging for cooling.

Either way - if their specification calls for this, you cannot bypass it on IP rating or NEMA alone.

Regards,

Craig

Register to Reply
Anonymous Poster
#6

Re: Sun Shade Protection

06/11/2009 7:56 AM

There instrument sunshades UV resistant and fire retardant,made for yr. requirement.

I know the company BULK srl in Italy www.bulksrl.it or there are also some in Germany.

Hope this could help you

Mauro

Register to Reply
Anonymous Poster
#7
In reply to #6

Re: Sun Shade Protection

08/03/2009 4:28 PM

Sun shades are often used to protect an instruments LCD display, which is vulnerable to damage from long term direct exposure to UV rays, even if temp considerations are not a problem.

Regards,

Bill

Register to Reply
Register to Reply 7 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); craigza (1); jack of all trades (1); Kilowatt0 (1); lyn (1); naveen_menon (1)

Previous in Forum: RTDs and Incorrect Temperatures   Next in Forum: pH Controller
You might be interested in: NEMA and IP Enclosures, AC Power Cords, IP Cores

Advertisement