Power loss calculations

05/01/2009 5:35 PM

here in Thailand when the developer builds a project, he has a transformer and meter installed by the Power Company.

He than must install an MDB and metering to individual plots, houses ect.

In most cases he reads the individual meters and bills at the rate on the main meter bill.

Now in these lean times they are seeing losses because no one took into account losses in the Transformer, cable losses, peak power charges, and so on.

Is there anyway I can calculate these losses, so they can pass them on to the end user. I would also need to provide an explanation that the customer would understand.

Any help welcome

Farang1

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Anonymous Poster
#1

Re: Power loss calculations

05/01/2009 9:33 PM

If you have gathered sufficient historical data then set up a table to compare the sum of the individual meter readings to the input meter reading and determine a factor that relates the two. Apply this factor to the individual bills explaining that it reflects the fact that the users' meters are not located at the outlet of the utility company distribution network and there are additional distribution costs to cross over from the utility to their meter.

Register to Reply Good Answer (Score 2)
Anonymous Poster
#3
In reply to #1

Re: Power loss calculations

05/02/2009 11:21 PM

Dear Guest,

Historical data aside. The individual customers may have a bad power factor and in most instances (at least here in the USA) individual meters DO NOT register this consumption ........... however ...... the utility company has meters that do register out of phase power. Users (at least in my area) are penalized for this and usually use capacitors to correct this problem. Industrial users can go the synchronous motor route as a second option. Mister CoGen Plant.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#2

Re: Power loss calculations

05/02/2009 8:27 AM

dear,

you need to install energy meters in all out going feeders at the source side, as well as ( at the consumer's side - which is always there )

difference is the losses.

Add to that, the transformer losses which come from the manufacturer;s test report.

__________________
Exploring the Science of Electricity
Register to Reply
Associate

Join Date: Feb 2009
Location: Songjiang District, Shanghai, China
Posts: 41
Good Answers: 4
#4

Re: Power loss calculations

05/03/2009 12:10 AM

Do I understand the following correctly?

1. The total gross power consumption of the project is metered by the power company.

2. The power consumption of individual users is metered at their sites.

3. There is a difference between the amount of power metered by the power company and the sum of the individual power meters, due to transmission losses and/or other factors.

4. You need a way to pass this difference onto the individual consumers in as equitable manner as possible.

Maybe this will work for you:

A. Calculate the difference (Power company meter vs. sum of individual meters; or Power company billing vs. sum of individual billings).

B. Spread the difference (the losses) among the consumers on a pro-rated basis. E.g. if you used 10% of the sum of individual metered power, you pay for 10% of the losses.

Just out of curiosity, where in Thailand are you working?

Cheeries !

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jun 2008
Posts: 11
#9
In reply to #4

Re: Power loss calculations

05/05/2009 5:41 PM

Hi,

I live in Koh Samui. I am an American and have had my business in Thailand for over 18 years. Contrary to a post on this subject, Thailand Is Not a 3 rd World Country.

I have lived here 33 years and never judge peoples on how they chose to live. Just because they don't have a TV or telephone, chose to live in the way there family lived long ago does not make them poor.

Thanks for the comments and help, we have begun a review of KW usage and will have an avarage loss by this weekend.

Thanks

Farang

Register to Reply
Associate

Join Date: Feb 2009
Location: Songjiang District, Shanghai, China
Posts: 41
Good Answers: 4
#10
In reply to #9

Re: Power loss calculations

05/05/2009 7:09 PM

Glad to hear that you are blessed to live in Thailand. I spent about 4 months in Mae Hong Son, and have a deep and abiding love for Thailand and the folks who are lucky enough to live there. If I am fortunate, I will return someday. I envision a lovely wife, a herd of adopted children, and a housebroken elephant named "Spot".

All the best to you Farang 1. and

Happy Trails !

Register to Reply Off Topic (Score 6)
Associate

Join Date: Jun 2007
Posts: 49
#11
In reply to #9

Re: Power loss calculations

05/06/2009 1:02 AM

Koh Samui is a holiday island and can hardly be compared with true 'rural' Thailand when discussing power supply issues.

Numbers of TV's/telephones are not the way to determine "poor" although most Thai people have both. Thai's are one of the richest nations in the world. Not financialy, but by their very nature and way of life. Many farangs should take a lesson in courtesy and manners from that whilst having the priviledge of living here.

I too have lived in Thailand for approaching 22 years and have been responsible for the growth of many companies here, and the education of many now world class Engineers.

Companies operated by farangs on Samui such as TechWorX appear to be already capable of solving the basic question you originaly asked, maybe you should be consulting with them.

KennyT

Register to Reply
Active Contributor

Join Date: Jun 2008
Posts: 11
#13
In reply to #11

Re: Power loss calculations

05/06/2009 5:48 PM

The sole purpose of my request was to get other professional's inputs to possible new technology as well as experience that other may have had in this area.

After all I am a professional that values and appreciates the input of others.

Register to Reply
Associate

Join Date: Jun 2007
Posts: 49
#14
In reply to #13

Re: Power loss calculations

05/06/2009 11:48 PM

That's fair enough, Pom-Kao-jai.

Chook-Dii Business.

KennyT

Register to Reply
Associate

Join Date: Jun 2007
Posts: 49
#12
In reply to #9

Re: Power loss calculations

05/06/2009 1:17 AM

The term used was "Emerging Country" not "3rd World.

KennyT

Register to Reply
Associate

Join Date: Jun 2007
Posts: 49
#5

Re: Power loss calculations

05/03/2009 12:42 AM

As a "farang" why are you making it your business? Do you live in Thailand or just here to do a job and then go home, wherever that may be?

Before you try and pass the inefficiencies of the Thai power system on to the consumer you must first look at giving a decent service to that consumer.

Thailand is an emerging country and the people have enough to contend with at the moment without "farangs" interfering and trying to make a name for themselves at the daily living expense of the indigenous people.

First get the power system working efficiently, dont pass corporate inefficiency downstream.

KennyT

Register to Reply
Anonymous Poster
#6

Re: Power loss calculations

05/03/2009 5:31 PM

the loses of the cable and transformer are prportional to the current taken by the consumer.

PL=Vl.I

P= V.I

from the supperposition action we know that the part of the lose of the transformer due to any plot depends on the amount of current taken by the same plot. the same current passing in the plot and the line connecting the plot to the board and the transformer is the same.

P=PL(V/VL)

let:

PL be reading of watthour meter

P be the losses in cable before the meter and transformer

V the voltage drop in cabel befor the meter and of the transformer.

Pt the total power consumed by the plot.

V= VB-VL

P=PL(VB/VL-1)

Pt=PL(VB/VL)

Let VB/VL for all the plots to be equal.

Now let the total meter reading of the transformer Be PT the PT=K(PL1+PL2+PL3+...)

Let the percentage of power by one plot be:

x= KPL/PT

Calculating the total power loses in the cable and transformes Pll:

Pll = PT- (PL1+PL2+PL3....)

Now we can find the Loses depending to each plot by multiplying the percentage of each plot found as x as above by Pll.

Now the total power consumption of each plot will be PL+Pll.

Register to Reply Off Topic (Score 6)
Active Contributor

Join Date: Mar 2008
Posts: 15
Good Answers: 3
#7

Re: Power loss calculations

05/04/2009 4:53 AM

Your bulk supply tariff will be always lower than that the charged tariff to the consumers.

In Pakistan, Consumer on bulk supply is categorized as under;

Consumer of connected load 5000 KW or more fall in B4 tariff.

Consumer of connected load 500 KW < 5000 KW fall in B3 tariff

Consumer of connected load 40 KW > 500 KW fall in B2 tariff

Consumer of connected load > 40KW fall in B1 tariff

If you observe rate per KWH (Unit), it seems that

B1 tariff is higher than tariff B2

B2 tariff is higher than tariff B3

B3 tariff is higher than tariff B4

Your selling tariff should cover the cost of all energy charges, power losses and operational and maintenance cost.

A good efficient system for houses (colony) is observed 98%-99% (which means the power loss is less than 2%).

Capacitor will increase your power factor ultimately reduction in apparent current results in reduction of power loss (copper losses).

Give the argument to the management that there is no power distribution system without power loss even on unity power factor.

Register to Reply
Anonymous Poster
#8

Re: Power loss calculations

05/04/2009 1:02 PM

You sum the individual meters in the development. To calculate the efficiency you divide the sum by the main meter reading. To calculate the losses subtract the sum from the main.

If the losses are greater than one would expect for line and transformer loses then it would be reasonable to expect that extra-ordinary losses are occurring.

In a public forum I do not wish to discuss how such losses occur, suffice it to say that they do. Explaining to the honest, metered customer that they are expected to pay for these ordinary and extra-ordinary losses is the heart of your problem. If the people do understand, then, they will be furious. In this country we ignore the problem, so the problem does not exist. Officially, there is no problem, people accept that explanation!

Register to Reply
Register to Reply 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (4); farang1 (2); Happy Fish (2); harry potter (1); KennyT (4); stahir (1)

Previous in Forum: Sizing a Cable from a Distribution Panel   Next in Forum: Help simulate a new loudspeaker box type

Advertisement