how to calculate the capacitive charging current of a cable with open circuit power factor of 0.1?
Re: capacitive charging current of a cable?
05/03/2009 12:02 PM
For calculating the capacitive current you need:
I=measured current
pf=0.1
it goes like: Icapacitive=sqrt(I-(I/pf)²)
Icapacitive is the capacitive current in open circuit.
the I/pf is the active component of the current, consumed in open circuit beacuse the electrical resistance if the insulation is not infinitely large.
The time is ......now
05/04/2009 2:52 AM
correction:
Icapacitive=sqrt(I²-(I/pf)²)
05/05/2009 12:58 AM
sqrt(I²-(I/pf)²)
I²<(I/pf)²
eg:- If I=10 & pf=.1
I²=100 & (I/pf)²=10000
Is it Possible?............
05/05/2009 2:15 AM
right. Sorry .
The thing was actually : Icap=I*sqrt(1-pf²)
where: I=measured current
pf- power factor
Icap= needed current
05/06/2009 12:10 AM
thanx
05/03/2009 8:49 PM
Use a scope to measure the rise time of the cable when a battery is suddenly applied.
Measure the capacitance of the cable with a meter or bridge. The R can now be calculated using t=RC. Now divide the voltage waveform from step one by R to get the current waveform. I think that will be the charging current that you are asking for.
05/05/2009 1:54 PM
Sorry; I need to add more to my answer:
For a transient voltage, the current flow will be the derivative of the voltage wave, ( i=dV/dt). So after capturing the voltage transient, take it's derivative and plot that.