Overvoltage in a Mains

05/04/2009 9:29 AM

Dear all,

I have come across a curious fault in a system on 11kv 3 phase 3 wire, supplied from the electricity company to distribution transformer 200kva - 275 mtr. away, & connected by 3c * 150 sq mm XLPE UE grade Under ground cable.

During a day time, operations are normal, voltages are normal - 400V 3 phase, 4 wire on LT side. Power capacitors of 20kvar * 3 nos. are connected fixed to thr distribution board. & are continuously ON.

We have provided a neutral contactor with the mains MCCB for DG change over.

What we have found that the coil of the Neutral contactor burns frequently, abnormally. Definitely, due to over voltages.

What could be the reason of such over voltages?

__________________
Exploring the Science of Electricity
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Overvoltage in a Mains

05/04/2009 11:43 AM

During the day when the load is high you utility voltage is normal. At other time the voltage is high because the load is low. The utility voltage regulation is lacking. Also the capacitors will cause a voltage rise when they are on line. You may want to measure the voltage with the cap off line and see it it helps.

Register to Reply Score 1 for Good Answer
Associate

Join Date: Apr 2009
Location: ras al khaima
Posts: 25
#2

Re: Overvoltage in a Mains

05/04/2009 2:11 PM

pls mention about your loads (what type of loads are you loading 1 phase or 3 phase). in case if single phase loads more than three phase loads this type of problem may happen. as you mentioned that magnetic netural contactor burning frequently. this type of problem happening because of temperature increasing on that contactor(core, coil etc., i think contactor coil slowly getting weak and making problem). check the return current as well as contactor rating suitable for return current.

Register to Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#4
In reply to #2

Re: Overvoltage in a Mains

05/05/2009 1:18 AM

dear,

contactor coil rating is 240v ac. proper.

LOAD ON SYSTEM : < 100 kva , transformer rating 200kva

nature of load : welding machines 15kva * 10 nos. , 20kva * 4 nos. , 8kva * ^ NOS>

__________________
Exploring the Science of Electricity
Register to Reply
Anonymous Poster
#3

Re: Overvoltage in a Mains

05/05/2009 12:58 AM

Check the load on each phase & balance the load.

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#5

Re: Overvoltage in a Mains

05/05/2009 7:12 PM

Harry

You have the answer to your question. Measure the voltage at peak loads, light loads and light loads with the capacitors off line. Then we can discuss the problem.

Register to Reply
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); harry potter (1); uticobala (1); wareagle (2)

Previous in Forum: Designing an Earth Mat   Next in Forum: ac or dc ? / Halogen bulbs

Advertisement