dear CR4 ,
my name is sansay samuel,iam electrical engineer and at present iam working in design and controls i need your help, i want to know how to calculate the voltage drop across the transformer , i want the steps and formulaes to calculate the heat dissipation and to select proper sizing of the enclosure give an example for this to beeter understand thanking you..
Re: voltage drop formulaes calculation across transformer
05/04/2009 9:43 PM
google "transformer voltage drop"
05/05/2009 1:23 AM
DEAR<
volt drop may not help you to calculate the heat dissipation.
Fixed magnetic losses * & Copper load losses I2R shall be able to help you to find out the heat dissipation & temperature rise etc...
Any way,
VOLT DROP IN TR> = E - Z*Ir
% regulation = (E - Z * Ir)/E
Exploring the Science of Electricity
05/05/2009 3:40 PM
offcourse voltage drop is a different factor than heat dissipation ,just i was asking you to provide for the selection of heater or thermostat to be sized according to heat dissipation thanking you for the formulaes u gave waiting for this ...