Current-Based Signals

05/06/2009 6:30 AM

Why is 4-20 ma preferred?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: electrical

05/06/2009 7:27 AM

<4mA or >20mA indicates instrument range error or circuit fault.

Current-based signals are practically immune to electromagnetic interference from other nearby circuits.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#2

Re: electrical

05/06/2009 8:07 AM

4-20 mA DC current is used to indicate sensor output or controller output, and the DC is not subject to externally induced currents by AC sources, since AC is required to induce current.

The reason 4 mA is used as the low end (rather than 0 mA) is typically used for ensuring that a process set off an alarm or shut down when no current is detected, since an open circuit between sensor and controller will also produce 0 mA current.

Some other common output/input current are 10-50 mA, 0-10mA, 0-50mA, but 4-20mA is the most common.

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: Current-Based Signals

05/06/2009 12:03 PM

I think the best way to think of it is to compare it to the other common alternative, 0-10VDC (or 0-5VDC). Using a DC voltage analog output signal has 2 main problems:

1) It is much much more susceptable to errors cause by noise, i.e. induced voltages from nearby AC circuits or RF interference.

2) It is more susceptable to voltage drop over long distances and drift due to temperature variations.

Using a current signal significantly reduces those issues to the point where they can be dealt with by monor adjustments in initial setup calibration. Then if you have decided on a current signal, the other issues posted above relate to why you want to use 4-20ma instead of 0-anything.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Anonymous Poster
#4

Re: Current-Based Signals

05/15/2009 6:29 AM

Why Not!?!

Ya gotta probem with that.

Register to Reply
Active Contributor

Join Date: Oct 2010
Location: Libya(Bangladeshi)
Posts: 15
#5

Re: Current-Based Signals

12/06/2010 9:22 AM

4-20 ma output is much more reliable than 0-20mA because of noise,vibration if nearby another machine works etc.

For example turbine flow meter its analog value set up is 200 cubicmeter/hour and counter will start to count ,If flow of oil in the pipe is 100% then output of sensor will read 20mA(200 cubicmeter/hour),If 75%(150 cubicm/hour),50%=100cubicm/H,25%=50 cubicm/H,

(If output of sensor is less than 25% then counter will not count,when exactly some flow in the pipe it will always more than 4mA.)

If it would start from zero ,then counter for Sump(Sump=total how many cubicmeter for 1dayor 2 day or 1 year) will count always even there is no flow of oil in the pipe ,because sensor output is always exist due external noise(nearby some motor can run),and its value can be 0.5mA or 1mA

Since our counter will work only if output of sensor more than 4mA.

So This type of meter (4-20mA) can reduce the error than 0-20mA

__________________
asadmawa
Register to Reply
Register to Reply 5 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); asadmawa (1); Bill (1); JRaef (1); PWSlack (1)