Lead acid battery

05/12/2009 3:05 AM

dear sir

In our 110/33/11 KV substation,we are using 55cells * 2 Volt =110V,300AH lead acid battery and one battery charger for protection of all equipments.

I dont have any materials like books or catalogues to correctly follow the maintenance of this batteries

That is

1)how much trickle current i have to give in float mode and how much boost current i have to give when battery is discharged condition.

2)what is the charged condition and discharged condition.

3)how to prepare the electrolyte?

In this regards, share your views and comments and if possible attach a material available please.

Kind regards

gova

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Lead acid battery

05/12/2009 3:26 AM

Is there a difficulty in contacting the original equipment supplier for this installation?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Aug 2006
Posts: 183
Good Answers: 2
#2

Re: Lead acid battery

05/12/2009 3:45 AM

Dear Gova

Tubular lead acid battery has to be float charged between 2.15-2.25 V/cell. According to the battery state of charge battery will automatically draw the require trickle charging current.

If battery is discharged then same has to be charged @ 2.7 V/cell at a max. current of 30 Amps. Though it can be charged @ 42 A also but then charging current has to be reduced to 18 Amps. after battery reaches 2.3 V/cell. Even better, slow charging continuously @18 Amps. is the best solution but time taken for charging will be higher.

We are an ISO 9001-2000 certified manufacturer of battery chargers & distribution boards for power plants and substations. We supply complete DC system with battery & are approved by leading consultants like EIL, Avant Garde, M.N.Dastur, MECON etc. and have installations in India & 12 other countries. For any further details, pls. feel free to contact.

Thanks and regards

Ashok Toshniwal, Bangalore, India. uni_insta@ dataone.in

Register to Reply Score 1 for Good Answer
Commentator
India - Member - New Member

Join Date: Nov 2008
Location: India
Posts: 72
#3
In reply to #2

Re: Lead acid battery

05/12/2009 4:01 AM

Dear Mr.Ashok

Thanks you very much sir.your explanation is nice and very useful to me.But i need general maintenance guide.If possible,please share in this forum.

If i have further doubt,I'll contact you sir.

Kind regards

G.Govardhan

Assistant Engineer

TNEB,Chennai

Register to Reply
Power-User

Join Date: Aug 2006
Posts: 183
Good Answers: 2
#4
In reply to #3

Re: Lead acid battery

05/12/2009 4:21 AM

Dear Govardhan

Thanks for acknowledging. I can send you the manual for Exide make tubular lead acid battery. I donot know how many people would like to have this on this forum, some may even consider it as off topic and therefore would prefer to send it to you. Kindly let me have your e-mail id.

Thanks and regards

Ashok Toshniwal, Bangalore, India

Register to Reply
Commentator
India - Member - New Member

Join Date: Nov 2008
Location: India
Posts: 72
#5
In reply to #4

Re: Lead acid battery

05/12/2009 7:44 AM

Dear sir

Thank you very much sir.

My emailID is:govavignesh_1976@yahoo.co.in

Kind regards

G.Govardhan

Chennai

Register to Reply
2
Power-User

Join Date: Jan 2007
Location: Johannesburg, South Africa
Posts: 230
Good Answers: 16
#6

Re: Lead acid battery

05/12/2009 2:27 PM

Hi Gova

Before we can help further, we need to know what type of cells your battery consists of - tubular plate vented, flat plate vented, Planté type, etc. If you don't know, contact the manufacturer. If you cannot, give us some details of the make/model if avaialable.

I'm a bit rusty on battery maintenance, though we also used them (I'm not directly involved with substations any more!). They are the hidden heart of a substation. From what I remember:

  1. Exact trickle charge requirements depends on the load and the way your charger measures the charging current. We don't boost charge our cells (see 6 below), but different types may require it - check with the manufacturer.
  2. Ensure that your ripple current at full charge is relatively low - a figure of <15% ripple Amperage rings a faint bell? Otherwise the plates could be damaged.
  3. Your battery should be fuse-protected against accidental short-circuits.
  4. Your battery should be protected against under-voltage (typically it must cut-out at 75% of full voltage, depending on your manufacturer's specifications). Voltages below that can severely reduce the life span of your battery, and may impact on the correct operation of your substation protection.
  5. We also measure the positive-to-earth and negative-to-earth readings monthly, these should be (in our specialised traction substation case) below 15V to ensure integrity of the protection system.
  6. Charging voltages and current are extremely important. We only use so-called Constant Voltage - Constant current chargers. For a 300Ah set that would mean charging a flat battery at no more than 30A until the correct voltage is reached (118,5V for Planté cells only, I think - different voltage for other types - check with manufacturer!). Then the voltage remains at say 118,5V and the current gradually reduces until full charge is reached.
  7. Ensure that the battery room does not exceed 25°C if possible - higher temperatures reduces battery life of certain types of battery.
  8. Clean terminals as they get dirty and corroded and apply petroleum jelly or whatever the latest technology is.
  9. Check water levels monthly or weekly and add as required. Excessive water use is probably an indication of overcharging. Charging voltages should be set with an accurate digital multimeter (if not fitted to the charger) - analogue dials are too inaccurate as a rule.
  10. We are not too fancy when it comes to recording, so we have a "battery book" that we record data in - every 3 months we take s.g. (specific gravity) readings and voltage readings of each cell, as well as the temperature of cell 1. Differences of cell voltage or s.g. is a warning that certain cells are about to fail. Protective eye wear and long rubber gloves are to be used when this is done. We also record charging voltage and current monthly.
  11. Also check for sedimentation 3-monthly, as excessive sedimentation at the bottom of a cell is indicative of a problem, and it could short out the cell or severely reduce it's Ah rating.
  12. Battery rooms are to be kept scrupulously clean, with an emergency water supply in case of acid spillage or explosion. Good ventilation (natural or flame-proof if forced?) is also essential.

We don't skimp on batteries - problems and shortcuts here can cost the unwary a substation if the protection is compromised!

Hope this guides you in the right direction.

Gideon

Register to Reply Good Answer (Score 2)
Register to Reply 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".