Circuit Breakers and Breaking Currents

05/13/2009 10:49 AM

why is circuit breaker making current is more than it's breaking current?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Circuit Breakers and Breaking Currents

05/13/2009 11:13 AM

It might have something to do with inductive starting currents when making, and arc suppression when breaking.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: Circuit Breakers and Breaking Currents

05/13/2009 1:39 PM

Electrical arcs represent a LOT of heat on the contact materials, i.e. the temperature of the sun right at the sruface where the arc jumps from/to. When making a set of contacts, an arc will jump the gap in the instant before the contacts close, but as soon as they close, it's over. When breaking, the arc is sustained for a longer period until the dielectric of the air is strong enough to iterrupt the flow of current. That breaking arcthen heats up the contacts a lot more, even to the point of vaoprizing the surface layer. That added heat is why you cannot break as much current as you can make.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
8
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#3
In reply to #2

Re: Circuit Breakers and Breaking Currents

05/13/2009 9:57 PM

To answer this question, let's first describe couple of concepts:

Breaking Current – The r.m.s value of the current at the instant of the contact separation is called the breaking current of the circuit breaker and it is expressed in kA.

Making Current: The peak value of the current at the time of making the contact of circuit breaker is called making current and it is expressed in kA.

Nature of Short Circuit Current: Over the time, the short circuit current goes with different state – (a) first 2 or 3 cycles is called sub-transient state, (b) next few cycles is transient state, (b) finally the steady state.

Generally, the short circuit current in sub-transient state is 1.8 to 2 times more than that of the steady state.

Circuit Breaker Fault Clearing Time: The circuit breaker has its fault clearing time which is the time elapsed between the instant of instance of fault occurrence and the instant of contact separation with final current zero.

Because of this time, actual contact separation of the circuit breaker occurs at time when the fault current reaches at its steady state. So, the breaking current of a circuit breaker considers the r.m.s value of the steady state of fault current.

Breaking current = r.m.s value of the steady state fault current

But, if a fault pre-exists and the circuit breaker is closed at this condition, the circuit breaker makes the contact with the fault current at the sub-transient state (or at best transient state).

Making current = The peak value of the sub-transient state fault current

= √2 x r.m.s value of the sub-transient state fault current

= √2 x 1.8 x r.m.s value of the steady state fault current

= 2.5 x r.m.s value of the steady state fault current

= 2.5 x Breaking current

So, the making current is almost 2.5 time of the breaking current.

Hope it helps.

-MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 8)
Register to Reply 3 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

JRaef (1); msamad (1); PWSlack (1)