Pls, what can be used to detect a phase to phase fault, if differential relay was not installed. I know an earth fault relay would not detect it but would an over current relay detect it.
Re: Phase To Phase Fault Detection
05/14/2009 11:40 AM
An overcurrent device supplying the circuit will trip. Most of these things can be fitted with auxiliary contacts these days.
Re: Phase-to-Phase Fault Detection
05/15/2009 5:48 AM
Dear all,
Phase-to-phase fault current has the value of 86.6% of 3 phase fault. In many cases, 3phase over current relay is can trip a phase-to-phase fault. If you need to detect and trip phase-to-phase fault with higher sensitivity, apply negative sequence (=unbalance)current relay, (ANSI device number = 46).
Regards
Akihito Shigeno @ JGC-Indonesia