Pls, what can be used to detect a phase to phase fault, if differential relay was not installed. I know an earth fault relay would not detect it but would an over current relay detect it.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Phase To Phase Fault Detection

05/14/2009 11:40 AM

An overcurrent device supplying the circuit will trip. Most of these things can be fitted with auxiliary contacts these days.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Oct 2008
Location: Jakarta Indonesia
Posts: 123
Good Answers: 7
#2

Re: Phase-to-Phase Fault Detection

05/15/2009 5:48 AM

Dear all,

Phase-to-phase fault current has the value of 86.6% of 3 phase fault. In many cases, 3phase over current relay is can trip a phase-to-phase fault. If you need to detect and trip phase-to-phase fault with higher sensitivity, apply negative sequence (=unbalance)current relay, (ANSI device number = 46).

Regards

__________________
Akihito Shigeno @ JGC-Indonesia