What is AHU configuration?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#1

Re: HVAC

05/17/2009 12:19 PM

AHU = Air Handling Unit. Mostly common in Air Conditioning application.

Basically a steam finned-tube radiator with a Blower. The steam enters from the top , the line tapped with a steam pressure reducing valve/ PRV(set very low between 1.0 bar-1.5 bar or as specified) & a temperature control automatic valve/TCV The bottom is drained by an automatic steam trap. The Blower blows and hot air is developed on the outlet which is then taken via a duct. The temperature sensor wherever installed open/closes the steam flow to the radiator( via the TCV )as per pre-determined set temperature on the controller. They come in various sizes/cfm and selected by the consultant/engineer on the model most suitable to him. The steam capacity then is determined by the size of the model/capacity AHU and selection made on sizing of the PRV & TCV + the Steam Trap. The equipments remains the same.

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Register to Reply
Register to Reply

Previous in Forum: running oxygen and acetylene plants   Next in Forum: Heat treatment of cold formed dished ends
You might be interested in: HVAC Services, HVAC Controllers, HVAC Ductwork

Advertisement