Neutral Size for 1/0.6 kV

05/18/2009 3:48 AM

why the cable manufactures produce the neutral size lower then phase conductor like 3x150+70mm2.

Register to Reply
Pathfinder Tags: 0123
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: Neutral size in 1/0.6 kV voltage

05/18/2009 4:18 AM

Have a look at previous posts on CR4 regarding this subject.

__________________
jack of all trades
Register to Reply
Participant

Join Date: May 2009
Posts: 3
#3
In reply to #1

Re: Neutral size in 1/0.6 kV voltage

05/20/2009 6:47 AM

thanks for answer, if it possible we will cut the Neutral, of below cross sectional area 3x150+1x70 mm2, and each cable will be installed in each phases (A, B, C) like 3x150mm2, if we use like this is it unbalanced load nonlinear will be appeared in phases or not and the code allowed.

Register to Reply Off Topic (Score 5)
Active Contributor

Join Date: May 2009
Location: Philippines
Posts: 23
#2

Re: Neutral Size for 1/0.6 kV

05/19/2009 4:08 PM

Replying to Forum Thread by hedayatullah_hotak:why the cable manufactures produce the neutral size lower then phase conductor like 3x150+70mm2.

Dear Mr. Hotak,

If the electrical loads in the panelboard are all 3-phase and are balanced, there will be zero current in the neutral conductor. And If the panel has a more 3-phase loads than 1-phase loads, then 1/2 size neutral is fine. However, if all the loads are 1-phase, there is a possibility that only phase A circuit breakers are all closed and all phase B & C circuit breakers are all open. If this is the case, the current in the neutral will be the same as the phase A conductor, and if the neutral conductor is sized 1/2, the entire neutral conductor will be overloaded and it will burn. If this is your case, your neutral should also be 150 mm2 or 4 x 150 mm2.

Regards,

Rudy C. Fernando

Philippines

Register to Reply