Transformer Impedence

05/18/2009 5:25 AM

Pls, can anyone explain to me in easy to understand way. Why is the impedence ( Z ) of a transformer written in percentage ( % ) and not in ohms.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jul 2007
Posts: 4448
Good Answers: 143
#1

Re: Transformer Impedence

05/18/2009 7:27 AM

In general, the use of Z% is related to fault currents. It provides an easy measure of how much fault current the transformer will try to pass when the secondary is shorted. For example, suppose you had a Z 20% transformer with a rated secondary current of 100A. The maximum short-circuit secondary current would then be 100A/0.20 = 500A.

Obviously this is not a very useful characteristic for, say, an audio output transformer where indeed the impedance might be given in Ohms.

__________________
"Well, I've wrestled with reality for 35 years, Doctor, and I'm happy to state I finally won out over it." Elwood P. Dowd
Register to Reply Score 1 for Good Answer
Associate

Join Date: Sep 2008
Posts: 31
#2
In reply to #1

Re: Transformer Impedence

05/19/2009 3:25 AM

Thanks alot. That was easy and very helpfull. Thanks.