Chillers - KW per Ton of Refrigeration

05/18/2009 7:03 PM

How can we calculate the KW per ton of refrigeration of a chiller? How much difference will be there between the air cooled and water cooled chillers in KW/TR?

Can anyone suggest me?

Register to Reply
Pathfinder Tags: KW/Ton of refrigeration
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Dec 2007
Location: Cypress Calif
Posts: 741
Good Answers: 23
#1

Re: Chillers - KW per Ton of Refrigeration

05/20/2009 12:38 AM

Hello Ramkumar Allu:

The best source is the manufacturers information sheet on the particular equipment.

The old rule of thumb used to be 1 hp= 746 W per ton of air-conditioning, this will still get you in the ballpark, but it's a very big ballpark. Efficiency of the machines vary by how heavily they are loaded, ambient temperature, and humidity.

As far as air cooled condensers versus watercooled, in general I would say water cooled condensers have a slight efficiency advantage, however in extremely humid conditions that advantage is largely lost, along with the watercooled condenser comes parasitic losses associated with the pumps.

However water cooled condensers are not necessarily used for increased efficiency per ton of AC, ductwork and building design concerns often favor remote chillers /air handlers , fan coils, Located in various parts of facilities or buildings, and the heat dissipation device i.e. cooling tower on a roof or some other convenient part of the facility.

__________________
"The reasonable man adapts himself to the world; the unreasonable one persists in trying to adapt the world to himself. Therefore all progress depends on the unreasonable man" George Shaw
Register to Reply
Anonymous Poster
#2

Re: Chillers - KW per Ton of Refrigeration

05/20/2009 3:37 AM

Hey,

The Energy in TR is calculated by multiblying the Flow of water in chiller cooler in USGPM by the diff in Temperatures in/out in degree Fehrenheit devided by 24 hrs for a value of an hour.

The electrical effecincy can be calculated by dividing the KW consumption of chiller motor by the Energy in TR.

Regards,

Ehab.

Register to Reply
Anonymous Poster
#3

Re: Chillers - KW per Ton of Refrigeration

05/20/2009 1:54 PM

I checked some product data about a Carrier Corporation modular chiller. The water cooled version has a full load efficiency of about 0.7 kW/Ton. The air cooled version has a full load efficiency of about 1.1 kW/Ton.

Register to Reply
Participant

Join Date: May 2009
Posts: 3
#6
In reply to #3

Re: Chillers - KW per Ton of Refrigeration

06/04/2009 3:34 PM

Is this electrical KW or Mechanical KW? Please clarify?

Register to Reply
Anonymous Poster
#4

Re: Chillers - KW per Ton of Refrigeration

05/20/2009 4:08 PM

I guess you all are referring to air conditioning. For -100°F brine, it'll cost about 8 KW/ton, since the latent heat of the refrigerant, ambient losses, compression ratios, compressor efficiency all change depending on the system temperature.

Register to Reply
Power-User

Join Date: Mar 2009
Location: O'er looking the silvery Tay
Posts: 255
Good Answers: 18
#5

Re: Chillers - KW per Ton of Refrigeration

05/23/2009 4:52 AM

Hi ,

Tons refrigeration effect is an old fashioned measure of compressor capacity.

1 Ton/hr= 12,000 BTU. divide by 3412 to get kWs = 3.52kW/hr

You will then have to make allowance for the COP of your machine and the operating conditions both (cold and hot side) to arrive at the overall performance of your machine.

Hope this helps.

__________________
If it ain't broke,leave it well alone .........until it comes looking for you!
Register to Reply
Anonymous Poster
#8
In reply to #5

Re: Chillers - KW per Ton of Refrigeration

01/11/2010 4:47 AM

what is 3412

Register to Reply Off Topic (Score 5)
Power-User

Join Date: Mar 2009
Location: O'er looking the silvery Tay
Posts: 255
Good Answers: 18
#9
In reply to #8

Re: Chillers - KW per Ton of Refrigeration

01/11/2010 9:56 AM

Hi Guest.

It is the number of Btus generated by 1kWh of energy. Therefore it is the divisor needed to convert to the CGS systemfrom the Imperial standard.

Massey.

__________________
If it ain't broke,leave it well alone .........until it comes looking for you!
Register to Reply Off Topic (Score 5)
Anonymous Poster
#7

Re: Chillers - KW per Ton of Refrigeration

07/20/2009 9:22 AM

Its is simple.Kw/ton is power consumption of chiller/tonnage of refrigiration of chiller in tons.For watercooled at full load it ranges from 0.6-0.7.For part load(IPLV or NPLV) best is around 0.4.The above is for centrifugal type.For aircooled at full laod it ranges 1.23.at part load it ranges to 0.9.Less kw/ton means lesser power consumption and more saving in operating cost.