Switchyards and Earthing Conductor Sizes

05/19/2009 11:59 PM

How can calculate the earthing conductor sizing for the switchyard of 400kV?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: earthing

05/20/2009 3:08 AM

It would be inadvisable for the earthing conductor to be of a smaller cross-section than the largest of the phase conductors, for a start.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Anonymous Poster
#2

Re: Switchyards and Earthing Conductor Sizes

05/21/2009 12:29 AM

I hope that you want to size the earthing conductor size for entire 400kV switchyard. Please refer IEEE-80-2000 clause 11.3. However, for conductor size depends upon, fault current and duration.

Register to Reply Off Topic (Score 5)
Active Contributor

Join Date: Mar 2009
Location: Makassar, Central Indonesia
Posts: 15
#3

Re: Switchyards and Earthing Conductor Sizes

05/30/2009 9:50 AM

Dear Rajesh,

Looks like you are dealing with HV Substation earthing system, that's why it isn't the same as the earthing conductor sizing at LV system.

In your case, the conductor sizing is depend on,

1. Rated System Voltage

2. Short Circuit Current Level ( e.g 16 kA, 25 kA, 31.5 kA or 40 kA ), usually for 400 kV system we choose 40 kA.

3. Step and touch voltage.

You can get the detail theory and calculation sample at :

1. IEEE 80-2000." IEEE Guide for safety AC Substation Grounding.

2. Power Substation Engineering. by John Douglas McDonald

chapter 11.3.6.2

Regards,

Stanyadji

Register to Reply
Anonymous Poster
#4
In reply to #3

Re: Switchyards and Earthing Conductor Sizes

05/31/2009 11:11 AM

hi thankyou very much for giving reply but i dnt have IEEE std 80 edition to calculateplease can u help regarding this?

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#5
In reply to #4

Re: Switchyards and Earthing Conductor Sizes

05/31/2009 11:17 AM
Register to Reply