Motor Name Plates and MCB Ratings

05/20/2009 10:28 AM

I'm confusing myself with Some nameplates of a motor here. On the name plate it says Amps 5-4.8 / 2.5-2.4 for this 1.5HP motor. How do I work out the MCB rating for this. Do I have to allow for 6x current on start up or is this part of choosing a correct mcb i.e ) Class C or D.

If someone could tell me simply how to work it out I would appreciate it. I imagine a C6 MCB would be fine ?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Motor Name Plates & MCB Rating

05/20/2009 10:40 AM

Is this a 3Ø motor?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster
#2

Re: Motor Name Plates & MCB Rating

05/20/2009 11:54 AM

yeah sorry 3 phase motor.

Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#3

Re: Motor Name Plates and MCB Ratings

05/20/2009 8:17 PM

Actually, you did not confuse yourself but you miss out some importance data's. You have a 3 phase motor with two type of winding connection. One is the "Star" point connection and the other connection is the "Delta" Connection.

If you look carefully at the name plate again, yo can see two type of voltage in the motor name plate. One should be showing 440 V and the other showing 220V.

If I am not mistaken, for "Star" point connection, your motor amps should be 2.5-2.4 Amp and the "Delta" connection should be 5-4.8 Amp. (Or it is the other way round)

Selection of MCB and Overload protection will depend on which type of motor winding connection that you are going to used.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Reply Score 1 for Good Answer
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#4
In reply to #3

Re: Motor Name Plates and MCB Ratings

05/21/2009 12:33 AM

"If you look carefully at the name plate again, yo can see two type of voltage in the motor name plate. One should be showing 440 V and the other showing 220V."

The calculation for your motor amps is as follows

If you used 440V supply for your motor; (Should be in "Star" Connection)

Power = 1.5KW

Amp = 1500/ (440x1.732x0.85pf)

Amp = 2.3 A

If you use 240V supply: (Should be in "Delta" Connection)

Power = 1.5KW

Amp = 1500/ (240x1.732x0.85pf)

Amp = 4.2 A

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Reply
Power-User

Join Date: Dec 2006
Posts: 346
Good Answers: 6
#7
In reply to #3

Re: Motor Name Plates and MCB Ratings

05/30/2009 7:53 PM

simon wan; many motors used in the USA, are 9 leads, with fixed star winding, for the low voltage connection with the remaining 3 windings, 6 leads,wired in series with the fix star winding for the 480 volt use. for low voltage the 3 winding are connected star, and
wired in parallel, 2 star winding in parallel are the low voltage connection. perry

Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#8
In reply to #7

Re: Motor Name Plates and MCB Ratings

05/31/2009 8:20 PM

Sorry, I thought most standard motor has 3 winding and 6 leads for selection for Delta or Star point connection. Never thought to have motor with 9 leads. I have seen one of these motor before but it was a very long time ago.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Reply
Anonymous Poster
#5

Re: Motor Name Plates and MCB Ratings

05/21/2009 4:23 AM

I think because it's a low motor rating, it will be just a Direct On Line Motor / On off Switch so should I choose a MCB 6x the nameplate current or will a 6C/D be sufficient?

Thanks for all your answers so far :-) Excellent Forum.

Reply
Power-User
New Zealand - Member - Kiwi

Join Date: Oct 2007
Location: Christchurch, New Zealand
Posts: 328
Good Answers: 29
#6
In reply to #5

Re: Motor Name Plates and MCB Ratings

05/21/2009 4:33 PM

Provided that you are using a thermal overload relay to provide thermal protection (highly recommended), the function of the MCB is mainly to provide the instantaneous short-circuit protection. If so, a 6A D-curve will definitely suffice if you are running in delta configuration, and will probably be ok if you are running in star mode too.

If you add up the cost of the thermal overload relay and MCB, you may well find that it is cheaper to buy a motor-protection circuit breaker instead - this combines both functions into one package that can be precisely adjusted to match the motor.

__________________
paulusgnome
Reply
Reply to Forum Thread 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); Paulusgnome (1); perry (1); PWSlack (1); Simon Wan (3)