Can we connect both Elec. & Inst. Earthing system in same grid.

05/21/2009 3:29 AM

Dear Sir,

If we can Connect both electrical & instumentation systems in the common earth grid & earth electrodes, what will be the impact on this?

In most of the cases i have practised with dedicated earthing system for instrumentation, but at present now i am doing one project, in that they are asking for combined earthing. can any one of you guide me???

Regards,

Dinesh

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Can we connect both Elec. & Inst. Earthing system in same grid.

05/21/2009 3:40 AM

Earth is earth is earth.

  • It is better, though not a requirement, to keep power earths and instrumentation earth wiring separate until the last connection onto the earth electrode system. The reason is that, if combined, the voltage drop along the combined earth conductor can, under power fault conditions, put a voltage onto the instrument earth system and that can have some peculiar effects on all the instrumentation. "Can", not "will", as these days most instruments are so bomb-proof that the effects are usually minimal.

Follow the specification "they" have provided.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Good Answer
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#2
In reply to #1

Re: Can we connect both Elec. & Inst. Earthing system in same grid.

05/21/2009 7:47 AM

Correct and GA,

BTW all instruments are not bombproof and we had quite a few computers damaged.

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#3

Re: Can we connect both Elec. & Inst. Earthing system in same grid.

05/21/2009 8:41 PM

Never and ever combined both Instrument Earth with Electrical Earth system togeather. In my previous company, I have problem with the PLC card for the instrument burnt. Finally, when I make a study on the erathing system, I found that the electrical earthing system and the Instrument Earthing system was combine togeather.

What happen is that, during the maintenance days, there will be some welding works in the area by the mechanical people and the problem with "them" (these peolpe) is they don't even care about they welding set earthing. They will earth their welding set any place convenion to them and start the welding works at any place they like.

At the end, the return high current from the point of welding, will flow every where and these current will find the lowest resistence path to flow back to their welding set. If your instrument is earth together with the electrical earth, I will sure that your instrument will burnt by the welding current.

At the end, I have seperate all the instrument earth with the electrical earth and burried a 1.2 meter x 1.2 meter x 10 mm thick copper plate for the instrument earth. Since then we don't have these problem with the instrument spoil or PLC card burnt.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Reply
Reply to Forum Thread 3 comments