Previous in Forum: How to Calculate Lobe Pump Head   Next in Forum: General
Axial Flow Fans and Altitude
05/26/2009 8:20 AM
Hi.. I am selecting an axial flow fan. My system requirement is 6700 cmh at 75 pa, at 0 ft altitude. Now, altitude is changed from 0 ft to 10,000 ft. Is there any impact on flow as altitude increases? if yes, please suggest at what parameters I shall design a fan at 0 ft so that it can deliver 6700 cmh at 75 pa and 10,000 ft altitude. Regards, Keyur
First do it and then talk about it
Good Answers: 137
Re: Axial Flow Fans and Altitude
05/26/2009 11:00 AM
Hello keyur
According to my calcs, at 10000 ft atm pressure is down from 1000 to 680mbar. With your fan as it stands ΔP drops to 75*0.68Pa = 51Pa, as ΔP is proprtional to inlet density (hence pressure). Actual flow (i.e. measured at the lower pressure) remains unchanged. If you increase fan speed by 1/√0.68 = 1.21, ΔP goes back to 75Pa (1.212*51 = 75) and actual flow to 6700*1.21 = 8110 cmh, and power drawn will (I think, haven't quite decided) increase by factor 1.21.
Cheers........Codey
05/26/2009 11:57 AM
Hi.. thanks for explanation but I am bit confused. As you mentioned, as altitude increases pressure drops but this is system pressure and I think it should remain constant. If I am wrong, please explain... Regards, Keyur Shah
Good Answers: 137
05/27/2009 7:02 AM
Hello keyur
Not sure what you mean by system pressure. I assumed the 75Pa requirement is a dynamic loss and after the system the air discharges to atmosphere. So at sea level the fan suction pressure and the system discharge pressure are both 1000mbar, at 10000ft they are both 680mbar. Is this correct?
If so, then my figures are :-
Sea level. Actual inlet flow 6700cmh. Fan inlet pressure 1000mbar = 100000Pa. Fan ΔP 75Pa. Fan discharge pressure 100075Pa. System ΔP 75Pa. System discharge pressure 100000Pa. Power drawn W.
10000ft - speed unchanged. Actual inlet flow 6700cmh. Fan inlet pressure 680mbar. Fan ΔP 51Pa. Fan discharge pressure 68051Pa. System ΔP 51Pa. (Fan and system ΔP both proportional to inlet density, sea level figure x 0.68). System discharge pressure 68000Pa. Power drawn 0.68W (flow as at sea level, ΔP x 0.68).
10000ft - speed x 1.21. Actual inlet flow 6700 x 1.21 = 8110cmh (proportional to fan speed). Fan inlet pressure 680mbar. Fan ΔP 75Pa (proportional to speed2). Fan discharge pressure 68075Pa. System ΔP 75Pa. System discharge pressure 68000Pa. Power drawn 1.21 x W (flow x 1.21, ΔP as at sea level).
Cheers.........Codey
06/02/2009 1:43 PM
Hello Keyur... ... A quick query:
Are you attempting to move a volume of air as in an exhaust stack? Or, is this volume of air intended for another purpose such as equipment cooling?
Sorry to be so late into the thread... ... out of town.
Regards
“Any sufficiently advanced technology is indistinguishable from magic.” Sir Arthur Charles Clarke
06/04/2009 7:36 AM
Hi, This is for equipment cooling.
Codemaster (2); GLB (1); keyur_197 (2)
You might be interested in: Axial Flow Pumps, Gas Flow Meters, Flow Meters