Controller and Recorder in Series
05/27/2009 9:54 AM
Hallo!
i have a transmitter(4-20 mA), honeywell controller UDC 2600 and minitrend recorder TVMQX, i connect them as shown below
i dont have any time to test, so that can any one tell me if this will work correctly
THNX SO MUCH
Good Answers: 54
Re: controller and recorder in series
05/27/2009 10:20 AM
If your transmitter (TX) is self-powered, this will work. Otherwise, you'll have to connect a 24Vdc power supply to the loop.
Next question: what's the input requirement for the recorder (in volts or millivolts). With a 10Ω resistor, your voltage at the recorder's input will be 0.04 to 0.2 volts. If this is what you need then there's no problem. If it's not, you'll need to change it.
Vmin = 0.004 × R
Vmax = 0.02 × R
regards,
Vulcan
05/27/2009 10:38 AM
thank u so much!
UDC controller and TVMQX are configreated as current input, so all what care me is to get 4-20 mA to these devices
THANX
05/27/2009 11:11 AM
If both the load devices are both 4-20mA input then omit the parallel resistors, otherwise the readings will be in error on the low side.
05/27/2009 11:38 AM
thnx for reply
UDC controller and TVMQX recorder catalogs show that resister must be installed at controller pins when configruted as currunt input (250 ohm for controller) and 10 ohm (for recorder)
05/27/2009 11:56 AM
In that case the controller is actually 1-5V input and the recorder is 40-200mV input. It is the external resistors, in this case, that determine the match of each device to the loop.
If this is the case, then the sketch is correct, though it is worth double-checking.