low voltage switchgear in Hydro powerplant

05/30/2009 7:34 AM

why is it necessary to have full-proof interlocking to ensure that different supplies and transformers are never operated in parallel?

India

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#1

Re: low voltage switchgear in Hydro powerplant

05/30/2009 8:44 AM

DEAR<
simple reason that different supplies on in coming side are not in synch. mode, i.e. not in same phase. if paralleled, short circuits will occur in control section.

__________________
Exploring the Science of Electricity
Register to Reply
Participant

Join Date: May 2009
Posts: 2
#2
In reply to #1

Re: low voltage switchgear in Hydro powerplant

05/30/2009 9:03 AM

yeah..dis one i know harry..i also replied this only to my boss..he said...no we may connect tahem in parallel for once...but it can create a disaster..

can u plz expalin me in detail ..i mean more elaborate ..

abt parapplel connection n all.

Register to Reply
Associate

Join Date: Oct 2008
Posts: 39
Good Answers: 1
#3

Re: low voltage switchgear in Hydro powerplant

05/31/2009 12:42 AM

Dear Friend,

Can you tell us what type of hydropower, we are about to comment. Is it micro, mini, small and large (above 10MW) hydro power plant?

Full proofing interlock with LV (Swgr & Transfo) should be done and should never be in paralleled in above 10MW hydropower. But, in mini down to micro, transfo paralleling can be done in LV side only. Many rated combined power (MW) plant are splitted into equal turbine generator; for example if the calculated "Q" gives you a 3MW then you can split this to 3 equal turbine generator, which is 3x1000kW. Then, the output of these 3 TG can be synchronized or paralleled into one (1) 3500kVA transformer. Some small hydro power project are doing this except for the large one.

The station and feeder transformers, which is LV power is not required a full proof interlock. Only control and protection system is requied.

Eren

Register to Reply
Anonymous Poster
#4
In reply to #3

Re: low voltage switchgear in Hydro powerplant

06/01/2009 2:53 AM

yeah ... m talking about mega hydroproject.. i.e. above 500 MW.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: low voltage switchgear in Hydro powerplant

06/01/2009 4:30 AM

To avoid this:

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 5 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); ereneduarte (1); harry potter (1); nesin (1); PWSlack (1)

Previous in Forum: Emergency lighting   Next in Forum: laser cutter for stones (granite)
You might be interested in: Hydro Turbines, Panelboards and Switchgear

Advertisement