current transformer

05/31/2009 12:55 AM

can anybody explains why current transformer blasts when secondary is open circuited. give correct explanation

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: current transformer

05/31/2009 5:57 AM

http://en.wikipedia.org/wiki/Current_transformer

Also see previous CR4 threads on this subject.

__________________
jack of all trades
Register to Reply
Guru

Join Date: May 2009
Location: S of LCD
Posts: 654
Good Answers: 30
#2

Re: current transformer

06/01/2009 12:19 AM

If by "blasts", you mean 'voltage spikes' or 'sparks':

A CT behaves similar to a car's ignition coil which discharges via the secondary, (to the spark plug), when the primary is open circuited. This is the simplist explaination I could find http://en.wikipedia.org/wiki/Induction_coil

A Tesla coil is the same working principal. http://en.wikipedia.org/wiki/Tesla_coil

If this hasn't answered - or put you on the path - come back to me.

note; the terminology of primary and secondary is always 'true' to: 'primary' is the supply/input and 'secondary' is the output.

Or it's about the direction of the process, not the coil wire thickness or number of turns. These are to do with VA ratio - not 'process direction'.

__________________
“Don’t worry, they usually don’t swim backwards.” Steve Irwin
Register to Reply
Anonymous Poster
#3

Re: current transformer

06/01/2009 12:24 AM

http://www.control.com/thread/1026220105

Register to Reply
Commentator

Join Date: Feb 2008
Posts: 59
#4

Re: current transformer

06/01/2009 1:15 AM

If you mean does the current transformer explode when the secondary is opened (circuit energized), it depends on the voltage of the measured circuit. If the CT is in a low voltage (120 - 600 volts) circuit, probably no "blast" will occur. However, if the circuit is much higher in voltage (say 13.8 kv to 500 kv) then if the secondary is opened the primary potential will develop across the secondary terminals and the insulation will fail causing a blast or worse. For this reason CT secondaries are always short circuited if the secondary wiring must be moved, opened, reconnected, etc. Hope this helps.

Register to Reply
Member

Join Date: May 2009
Posts: 7
#5

Re: current transformer

06/01/2009 7:27 AM

Regarding current transformers (CT), they differ from your normal potential transfomer (voltage ) in that the primary current depends entirely on the load on the system and not on the secondary load.Therefore if the secondary is opened while the primary windings are carrying a heavy load, the demagnetising effect of the secondary current will no longer exist and there will be an increase in the flux in the secondary circuit, this could very well puncture the insulation or produce a dangerous shock to anyone coming into contact with it. therefore the seondary of CT should never be opened while the primary is energised. I hope this helps.

Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#6

Re: current transformer

06/01/2009 7:35 AM

give correct explanation

Defines it as close as anything to be a home work. At my times at least the questions (in home work or in exams used to end like this.)

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply
Guru
Engineering Fields - Electrical Engineering - New Member

Join Date: Oct 2007
Location: Sour Lake, TX 30°08'59.68"N 94°19'42.81"W
Posts: 675
Good Answers: 13
#7
In reply to #6

Re: current transformer

06/01/2009 1:32 PM

The subject came many times. Students, trying the easy way to answer the questions to their homework. Well, what if is the instructor the one having difficulties answering his own (or compiled from books) questions?

__________________
Bridge rule #1: Nobody is as good as he thinks about himself nor as dumb, as his partner thinks...
Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#8

Re: current transformer

06/01/2009 11:57 PM

There was a related thread started yesterday on short-circuiting CT's prior to removing the load. Answers to it explain your question. However, this sounds like a homework assignment. Please explain why you are asking this question and also look at the other thread. If you can give a good reason for not understanding, then we'll continue.

Regards--John M.

Register to Reply
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#9

Re: current transformer

06/02/2009 6:23 AM

Mate, when you say Blasts, i presume you mean burn out!

A current transformer is like any other transformer, the only difference is that the primary winding only has one winding, the one going through the CT. The secondary which is your current transformer, has hundreds if not thousands of windings, so when the CT is open circuit, the voltage generated in the secondary winding (your CT) can get very high, causing a total breakdown in the insulation of the CT. If you have to service a CT, i recomend that you either disconnect the power or short out the terminals of the CT to avoid failure, any other action is asking for failure. Simple croc clips across the terminals of the CT will allow you to do any repairs further down the line without damage to to CT. Just remember to remove the croc clips when you have finished you service work. Cheers Joe Sparky

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#10

Re: current transformer

10/10/2009 12:29 PM

Dear Mr.Rukmagoud,

The answer for your question, WHY CURRENT TRANSFORMER BLASTS WHEN SECONDARYIS OPEN CIRCUITED in simple terms, is,

THE VOLTAGE IS MULTIPLIED BY THE RATIO OF THE CURRENT TRANSFORMER.

For example, if you use 5000/5 RATIO CURRENT TRANSFORMER, THE RATIO IS

1000, AND IF THE VOLTAGE IS 420, THE TERMINAL VOLTAGE AT THE LOW CURRENT

SIDE WILL BE 420 x 1000 = 4,20,000 Volts, and this high voltage results in blasting of

the transformer.

DHAYANANDHAN.S,

CR 4 MEMBER,

INDIA.

Register to Reply