Connecting a 50-Hz Motor to a 60-Hz Power Supply

06/04/2009 12:20 PM

what would happen to a 50hz motor connected to a 60hz supply. the motor is 440v 3 ph 8amps

Register to Reply
Pathfinder Tags: 50hz motor to 60hz
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Participant

Join Date: Jun 2009
Posts: 4
#1

Re: motor 50hz to 60hz supply

06/04/2009 2:36 PM

Its synchronous speed will be 6/5 times the 50 hz value. Due to the increase of impedance with frequency there may be a small drop in starting torque. As you are not raising the input voltage the output power will be reduced at maximum slip.

Register to Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#3
In reply to #1

Re: motor 50hz to 60hz supply

06/06/2009 10:23 AM

Further,

motor gets heated up more due to more hysteresis losses .

__________________
Exploring the Science of Electricity
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: motor 50hz to 60hz supply

06/04/2009 3:16 PM

Also see the numerous previous CR4 threads on this subject.

__________________
jack of all trades
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#4

Re: Connecting a 50-Hz Motor to a 60-Hz Power Supply

12/27/2009 11:58 AM

Dear Mr.Trev1,

1. The impedence will be more and hence impedence voltage drop will be more by 20%.

2. Speed will be more by 20 % and unbalance force will increase by 44% over and above the forces experienced while running on 50 cycles supply, hence increasing the danger of rotor and bearing failure,if lubrication is not taken care.

3. over heating of motor will take place on account of extra impedence. Perhaps motor also will trip if relays are not taken care.

DHAYANANDHAN.S

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5

Re: Connecting a 50-Hz Motor to a 60-Hz Power Supply

12/27/2009 4:05 PM

I have lost count, but I'd say this is the SINGLE MOST ASKED QUESTION in this forum. I'd venture we are at over 100 queries.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply