Disconnecting an Ammeter from a Current Transformer (CT)

06/05/2009 12:59 AM

What are the steps that would take before disconnecting ammeter permanently supplied from a current transformer?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Member

Join Date: Feb 2009
Location: Australia
Posts: 7
#1

Re: steps before disconnecting ammeter

06/05/2009 2:20 AM

Haven't done this before...(So I might be wrong)

But definitely, Short out your CT circuitry, THEN remove the meter.

And if you could turn off the power in the first place, do that first.

Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: steps before disconnecting ammeter

06/05/2009 2:33 AM

http://cr4.globalspec.com/thread/38424/Disconnecting-Ammeters-from-Current-Transformers

__________________
jack of all trades
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: steps before disconnecting ammeter

06/05/2009 3:05 AM
  1. Isolate power to the equipment.
  2. Disconnect and remove ammeter.
  3. Blank-off ammeter panel hole so as to maintain ingress protection rating of the panel.
  4. Either short-out the output terminals of the current transformer, or remove it.
  5. Close panel door and re-energise.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#4

Re: steps before disconnecting ammeter

06/05/2009 3:25 AM

Haven't you read CR4. We had just discussed it last week.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Reply
Active Contributor

Join Date: Sep 2007
Posts: 21
Good Answers: 1
#5

Re: Disconnecting an Ammeter from a Current Transformer (CT)

06/05/2009 11:34 AM

It should first be understood that a current transformer is normally shot-circuited in operation. The secondary current produces a powerful magnetic counterflux. If this disappears for some reason; low load or disconnection of the measuring instrument as in the case being discussed, the primary current would generate a very high magnetic flux. This would overheat the core and generate an excessive voltage in the secondary winding, possibly damaging the insulation.

For this reason no fuses may be fitted in the secondary circuits of current transformers. Whenever the measuring instrument is disconnected, the secondary must be shorted across first. An easy, efficient and convenient way of doing this is through the use of shorting terminal blocks on the secondary of current transformers, which automatically short circuits the instrument transformers when the load is removed.

__________________
One does not need a mirror to look at what one is wearing on the wrist
Reply
Reply to Forum Thread 5 comments
Copy to Clipboard

Users who posted comments:

jack of all trades (1); PWSlack (1); Simon Wan (1); SmileyJack (1); solaaderinwale (1)

Previous in Forum: Coordinating Relays   Next in Forum: Substations and Maximum Demand

Advertisement