Changing the Voltage for an Air Compressor

06/05/2009 9:17 AM

I have I have air compressor it s 380 volt how can I change it to 230 volt ( it s 3 phs)

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Changing the Voltage for an Air Compressor

06/05/2009 9:21 AM

By getting in touch with the original equipment manufacturer, and following their recommendations.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#2

Re: Changing the Voltage for an Air Compressor

06/05/2009 10:14 AM

Assuming your 230v supply is 3-phase, 230v phase-phase, if the motor is 380v Y, 220v Δ, just connect in Δ. (220 and 230 are near enough)

If it's 380v Δ, 660v Y, you need to change the motor.

Cheers..........Codey

__________________
Give masochists a fair crack of the whip
Register to Reply
Anonymous Poster
#3

Re: Changing the Voltage for an Air Compressor

06/05/2009 11:30 AM

That motor seems to be a 380V 50Hz. 3Ph. and should be ready to run on 440V 60Hz. 3Ph. with no change, but for your supply which is 230V you would need to do these connections in your motor IF your motor has 9 leads:

For a Y connection: Conect 4 & 5 & 6 together and isolate; then connect 1 & 7 to phase 1. Connect 2 & 8 to phase 2. And connect 3 & 9 to phase 3.

For a Delta connection: Connect 1 & 6 & 7 to phase 1, connect 2 & 4 & 8 to phase 2 and connect 3 & 5 & 9 to phase 3.

If your motor has only 3 leads, then it is not dual voltage and you've gotta change it.

Yahlasit

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#4

Re: Changing the Voltage for an Air Compressor

06/06/2009 3:46 AM

Buy a single phase motor of the same power....or bigger.....sell the old motor to finance the new/second hand one....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Register to Reply 4 comments
Copy to Clipboard

Users who posted comments:

Andy Germany (1); Anonymous Poster (1); Codemaster (1); PWSlack (1)

Previous in Forum: Maximum Current from Single-Phase Power Supply   Next in Forum: Transformers: Liquid Dielectric or Not?

Advertisement