Orifice FT and CV

06/11/2009 5:08 AM

When orifice DP FT is used in the process line, It is placed before the control valve in the process line. it is because that rated DP should be created along the orifice plate, so that correct flow can be measured.

If vortex or electro magnetic flow meteres are used in the process line. can we use this meters after the control valve, so that controlled flow is measured.?

what happens If vortex and electromag FT are used before the control valve.?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: orifice FT and CV

06/11/2009 5:17 AM

It is to do with making sure that the disturbances in the flow streamlines have enough pipe length to dissipate, so that the flow has returned to normal after that point. Looking at most flow instruments in catalogues, they will have upstream-of-fittings and downstream-of-fittings criteria that the manufacturer needs to state to ensure rated instrument accuracy under the user's conditions.

It has little to do with the type of instrument, though the criteria for different instruments and different manufacturers may vary.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Participant

Join Date: May 2009
Location: Paris, Arkansas in early process of relocationg to Arizona
Posts: 3
#2

Re: orifice FT and CV

06/11/2009 8:00 AM

Fully agree with previous comment. Its important to fully understand the process medium and range of concern. Additionally, the term "Snubber" as used in process line intrumentation, is a fancy yet misleading name for an orifice-which application and placement result in a steady reading--instead of an oscillating and depending on process medium, sensor type and affects on flow in a line with many elbows and such with resultant pertabations of flow in or around area of sensor placement. Hope I didn't confuse the issue.

Register to Reply
Power-User

Join Date: Nov 2008
Location: Port Glasgow, Free Republic of Scotland
Posts: 360
Good Answers: 30
#3

Re: Orifice FT and CV

06/12/2009 7:24 AM

Control valves provide a large disturbance to flow and usually meters had to be located a significant length downstream of them to allow for the flow to have settled down (unless flow straighteners are used). This is one reason for locating meters upstream of the valve. Also by locating the meter upstream you can be more certain that there will be no flashing across the meter which will almost certainly invlaidate the readings. My personal preference would be to have the meter upstream for this reason.

As flows change the pressure downstream of a control valve will change more than the upstream pressure (hydraulic losses vary with the square of flow at 50% flow the hydraulic losses are 25% and so the pressure drop on the CV must pick up this lost hydraulic losses). By locating the meter upstream you maintain a more constant condition and one closer to that for which the meter was specified so its reading should be more reliable for liquids this isnt an issue but for gases where density (which is proportional to pressure) is key to the metering it is a factor.

You also mention that having the meter downstream allows you to measure the controlled flow - surely if there are no branches in the piping it doesnt matter whether you measure up or downstream?

__________________
Free advice guaranteed or your money back
Register to Reply Score 1 for Good Answer
Associate

Join Date: May 2009
Posts: 41
#4
In reply to #3

Re: Orifice FT and CV

06/12/2009 7:50 AM

Thank you for your answer sir. it was a good explanatory one. once again thankyou

Register to Reply
Active Contributor

Join Date: Apr 2009
Posts: 20
#5

Re: Orifice FT and CV

06/12/2009 11:14 AM

With either the oriface plate or the mag flow meter you have to have a full pipe. You can measure either upstream or downstream from the control valve if you can guarantee that the pipe will always be full, even at low flow conditions. Different straight pipe upstream/downstream lengths are recommended for the different flow meters. Mag flow meters are pretty forgiving if these recommended lengths are not adhered to. Generally mag flow require 3 upstream and 5 downstream pipe diameters of straight pipe; oriface plates are generally stated as 5 upstream and 10 downstream.

Register to Reply
Power-User
South Africa - Member -

Join Date: Nov 2008
Location: Johannesburg
Posts: 295
Good Answers: 12
#6

Re: Orifice FT and CV

06/15/2009 2:50 AM

Hi there,

All very good answers.

Remember a control valve will cause turbulant flow downstream. You can locate the FE downstream of the control valve - but make sure you have enough pipe diameters to do this so that by the time the flow gets there it has recovered.

The same applies to putting the FE upstream of the control valve. The FE will cerate turbulant flow as it passes through the element. You then need to make sure that the control valve is placed with sufficient pipe diamteres away from the element. If not you could end up with flashing or cavitation in the valve.

This applies to all flow measurement types. A good way to get an idea of this is to take your process data, both for the valve and the flow element/meter and calculate the Reynolds number for each. This will help you determine the flow characteristic. With these numbers in hand you will have a better picture.

Regards,

Craig

Register to Reply
Active Contributor

Join Date: Jul 2009
Posts: 10
#7

Re: Orifice FT and CV

07/23/2009 5:26 AM

we can use DP FT before control vale but 8 diamter of pipe upsteam orifice and 12 diameter of pipe downstream of orifice should be straight. and flow measure against orifice of gas is better than othe meter. by ranjha

__________________
This is good place where technical people share their knowledge
Register to Reply
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments: