Live-to-Earth

06/11/2009 8:09 AM

is it acceptable to test live-to-earth conductors, then continue with the work when the test equipment reads zero? y/n and why?

please respond trying to finish module today....

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Systems Engineering - New Member Popular Science - Weaponology - New Member

Join Date: Jun 2006
Location: Borrego Springs
Posts: 2636
Good Answers: 62
#1

Re: Live-to-Earth

06/11/2009 8:33 AM

Sounds like homework.

We'll help with homework - we won't DO homework.

Come back when you have given it some thought and research on why it might or might not be a good idea and we'll help.

__________________
"If you want to get somewhere else, you must run at least twice as fast as that!"
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Live-to-Earth

06/11/2009 8:49 AM

<...continue with the work when the test equipment reads zero...>

A correct procedure would be:

  1. Lock-off the circuit being worked on.
  2. Test that the test equipment is working.
  3. Test that the locked-off circuit is dead, using the tested test equipment.
  4. Test that the test equipment is still working, by re-testing it on a live circuit.
  5. Issue Permit-to-work to the individual leading the work on the dead circuit, preferably handing the individual the key to the lock so that it can be returned when the permit is either cancelled or completed.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#3

Re: Live-to-Earth

06/11/2009 3:50 PM

Well its more ideal than performing the work and then testing to see if the conductors are live.

Don't laugh you know most of us have done this at some stage.

__________________
jack of all trades
Reply