Hello guys!!! Just want to ask what will happen if i just connect two wires(two lines) instead of three in a three phase delta connection for motor? Will these connection run? Any problem on these set up?
Re: Can i used two phase to run 3 phase delta motor
06/12/2009 12:51 AM
No you can not. The motor will attempt to produce the required power from one winding (on delta connection), will overheat and result in an insulation failure in that winding (called a single phase failure)
Re: Can i used two phase to run 3 phase delta motor
06/12/2009 2:02 AM
You can try it with the connection of two wires(two lines) instead of three in a three phase delta connection for motor but just for a short period of time. The motor will run either forward or reverse direction.
The only different is that the motor will operate in unbalance magnetic field and voltage due to the two phase supply to the motor in delta connection. The speed of the motor will reduce and gradually and the motor temperature will increase slowly.
Sometime, we do have this problem of 2 phase power supply to the roller table motor due to one of the phase cable under the roller table damage and the motor is running on 2 phase. Sometime it goes reverse direction and sometime it go forward direction.
__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Re: Can i used two phase to run 3 phase delta motor
06/12/2009 2:44 AM
You may connect the motor the same as a single phase motor, with capacitor and supply with 2 phase. The motor however will only produce about a ½ of the 3 phase power rating
Re: Can i used two phase to run 3 phase delta motor
06/12/2009 2:54 AM
That true. The motor torque will be less than the normal motor torque
__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Re: Can i used two phase to run 3 phase delta motor
06/12/2009 3:15 AM
The motor will stall, and either:
Its overload will operate, or,
The circuit protective device in one or both of the connected phases will operate, or
If neither of these happens, the motor will self-destruct. Have a CO2 fire extinguisher handy.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Re: Can i used two phase to run 3 phase delta motor
06/12/2009 3:32 AM
Transfrom the two phase to three phase and then use.
As it is - no you can not, efficiently and without the high probability of burning it.
But the transformation is easy and easied if you have the neutral available and the supply corporation allows you to use such an unbalanced loading.
__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Re: Can i used two phase to run 3 phase delta motor
06/12/2009 5:12 PM
There is a semantics issue here with regards to what you are referring to as "2 phase". There is such thing as true 2 phase power, but it is extremely rare. It is a legacy polyphase system left over from the earliest days of electrification, but still exists in parts of Philadelphia and Niagara Falls as far as I know. True 2 phase power uses 4 wires and the phases are 180 degrees separated from each other, or really, 90 degrees from one pole to the next.
If you are referring to 2 phases of a 3 phase system, that is technically not 2 phase power, but it is often mistakenly referred to that way in IEC terminology. In the US, we call that single phase. But that is slightly different again from distributed 1 phase power in the US, where the Line-to-Line relationship is 180 degrees out.
In a situation where we are looking at 2 out of 3 phases; A 3 phase motor will RUN if one phase is disconnected after it was already spinning, but it will only put out 58% of it's available torque and as such, slip will increase under load and the motor will likely overload. If you attempt to Start it with only 2 of 3 phases, it may try to start, but as mentioned by others there is no way to predict the direction of rotation. The 2 connected phases are separated by 120 degrees on one side and 240 degrees the other way. if the contactor connects when there is a 120 deg. separation, it may try to turn one direction, but if it connects when there is a 240 deg. separation, it may try to go the other way. But again, torque is reduced to 58% so if it needed LRT to accelerate, it isn't likely to start at all.
In a situation where you try to feed a 3 phase motor from a US 1 phase supply, where the line-to-line voltage separation is 180 deg. out, the motor will not even try to rotate at all without mechanical assistance because there is no relative phase rotation.