Diversity Factor for Electrical Design

06/12/2009 4:14 AM

is there any international standard that can be used to derive diversity factor for continuous load, intermittent load and standby loads

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: diversity factor for electrical design

06/12/2009 6:03 AM

No. Diversity is installation-specific.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#2

Re: diversity factor for electrical design

06/12/2009 6:15 AM

There is a NEC guide i think article 220 or so that talks about it, but in general terms as I remember. This is all by the experience of the power company.

check this for some idea

http://www.tpub.com/content/armyengineer/TM-5-811-1/TM-5-811-10013.htm

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#3
In reply to #2

Re: diversity factor for electrical design

06/18/2009 5:00 PM

Diversity factor applies to the loads that are not run simultaneously (noncoincident loads). The NEC 220.60 applies in this case.

The NEC 220.60 states "Where it is unlikely that two or more noncoincident loads will be in use simultaneously, it shall be permissible to use only the largest load(s) that will be used at one time for calculating the total load of a feeder or service".

Depending on the continuous or intermittent nature of the load, you need to apply factor 1.25 or not.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply