Anonymous Poster

KVA to Amps

06/12/2009 5:53 AM

For a 725 KVa DG set,how much load i can put.also send me the KVA factor conversion in to amps.

Regards

Siddu,

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: KVA to Amps

06/12/2009 6:01 AM

<...725 KVa DG set,how much load...>

No more than 725kVA

<...the KVA factor conversion in to amps...>

Divide by the voltage.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#2

Re: KVA to Amps

06/12/2009 6:35 AM

Assuming a normal motor power factor of say 0.80 (the load power factor you should know approximately) - the load will be 580 KW that is if you mean this to be the load.

The other part is already as in #1

KVA = 1000 x V x I

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#3
In reply to #2

Re: KVA to Amps

06/12/2009 8:43 AM

It is three phase load.factor 1.732 is missing

__________________
To avoid crticism do nothing,say nothing,be nothing
Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#5
In reply to #3

Re: KVA to Amps

06/12/2009 12:28 PM

You are right

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Reply
Anonymous Poster
#4

Re: KVA to Amps

06/12/2009 9:52 AM

Todays DG sets- Sold in India can safely handle upto 0.8 times the rated load, meaning 0.8*725= 580KVA.

DG Sets can also perform at full rated power for upto 60 minutes without any issue, but you would rather be safe and run the same UPTO 580KVA.

Am not an Elec Engr, but do run more DGs than most people have- and this thumb rule works for me.

KD

Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#6

Re: KVA to Amps

06/12/2009 9:02 PM

For 725KVA Diesel Generator, the total output current that is available is approximately 1000Amp base on 415V and assuming that the efficiency of the generator is 100% efficiency. The above calculation is in ideal stage.

The formula is as follows;

KVA=Voltage x Current (I) x 1.732 x Eff %

In actual, a new diesel generator can generated about 96% of the total KVA due to the losses in the generator such as electrical losses and mechanical losses. Therefore, you will get about 94% to 95% of the efficiency of the generator output. As the generator get older the efficiency will also decrease and the output current will also become less.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Reply
Commentator

Join Date: Nov 2008
Location: S.E. Asia
Posts: 91
Good Answers: 1
#7
In reply to #6

Re: KVA to Amps

06/13/2009 9:46 AM

I agree with this & would also like to add that the type of load is important. For example, a genset that feeds a UPS (a non-sinusoidal type of UPS) should be derated according to the level of harmonics generated by the UPS. As a general rule, a derating factor of 1.5 is safe for all situations (this is a very broad estimation). Eg. Generator is calculated to be able to supply (at 100% duty cycle) 1MVA. However, it could only safely supply about 500KVA to a harmonic load.

__________________
"If you try to keep a leg each side of a barbed-wire fence, you'll do yourself a mischief." - Joh Bjelke-Petersen.
Reply
Commentator

Join Date: May 2009
Location: Centurion, South Africa
Posts: 87
Good Answers: 5
#8

Re: KVA to Amps

06/15/2009 2:56 AM

Remember the type of load you are supplying will also have an influence on how much load you will supply with the unit.

If you are supplying motors only you need to consider start up currents. Depending on what percentage load you are already applying to the GD, you may run into a situation when attempting to start a motor the motor may not reach full speed.

During the start up of this motor (7 X Full load current) you may overload the GD, and the output voltage of the gen set will drop resulting in a torque loss in the motor ( (Vn/Vr)³, see previous threads on this). Should the inertia of the load on the motor be high, the motor will not reach full speed with the reduced torque available. The motor should eventually trip by the protection relay. This scenario may also happen should you attempt to start a large(400kW) motor, without any other load applied to the GD.

If you have a combination of motor and resistive loads (lighting) you want to do motor starting first and then switch on the resistive loads (no starting currents) to avoid the above scenario.

__________________
R T F M .......
Reply