How to calculate the rating and size of cable?
Re: Cable size
06/12/2009 6:23 AM
Use British Standard 7671, like all the others that have asked.
Re: Cable size
06/12/2009 6:29 AM
I require the formula for calculting the rating and size of cable.
Re: Cable size
06/12/2009 6:36 AM
The first Guest is looking for BS7671. Teamwork makes for a better search.
Good Answers: 103
Re: Cable size
06/12/2009 6:38 AM
cable size = f(conductor diameter, current carrying capacity,resistivity, conductor thermal conductivity, insulation thickness, insulation thermal conductivity, insulation maximum temperature(class), ....)
is it worth it?
Re: Cable size
06/12/2009 7:55 AM
Hi,
I give you a practical tip: for a short distance (<500m) the current rate should be 2A/mm2. for longer distance, it should be less than 2 (1-1,5). for VSD, it should be 1 (or less) depend on each application. for very short distance (some metter) you can increase the number but should not exceed 7A/mm2. Remember: this tip apply to Copper cable only. for Alumin cable, the number should devide 3 or 4.
Regards
Re: Cable size
06/12/2009 8:41 AM
why do we have to repeat refer earlier threads.u will find a lot of info if u refer to earlier threads