Anonymous Poster

Destructive Harmonics Mitigation and recyclingback to useful energy

06/12/2009 10:52 PM

Anybody who knows how to mitigate destructive harmonics, 3rd and fifth, and somebody claim that they can recycle back to useful energy utilizing a zigzag transformer.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#1

Re: Destructive Harmonics Mitigation and recycling back to useful energy

06/14/2009 9:06 AM

Stop listening to snake oil vendors / perpetual motion salesman. Harmonics are not energy. They are a distortion of the waveform. They behave like bad power factor. You cannot turn 10KVAR of lagging power factor into 10KW even with power electronics converters and even less with any type of passive transformer.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Reply
Power-User

Join Date: Aug 2008
Location: West Virginia
Posts: 185
Good Answers: 12
#2

Re: Destructive Harmonics Mitigation and recyclingback to useful energy

06/14/2009 10:01 AM

Most harmonics are caused by large non sinusoidal loads connected to 3 phase power. Things like switching power supplies and electronic ballasts. This usually requires considerable up sizing of the neutral wire and special harmonics rated transformers. Prevention is pretty much the only way do deal with this type of problem. Do you have any idea what is generating these harmonics?

Reply
Anonymous Poster
#3

Re: Destructive Harmonics Mitigation and recycling back to useful energy

06/14/2009 10:18 PM

Guest,

As stated in replies already submitted harmonics on power network are generated by non sinusoidal loads such as switching power supplies, inverters, and variable speed drives.

I am sailing as Chief Engineer on a ship employing SCR drives to power 2- 2150 HP propulsion motors. Harmonics are a significant problem.

SCR ships service AC to variable voltage DC is accomplished with a 12 pulse converter, creating significant 5th, 7th, and 11th order harmonics.

Solution is filters consisting of 3, series L-C circuits tuned to the 3 harmonic frequencies providing a low impedance path for the harmonic components back to the source (SCR Drives) through a resistor network to be dissipated as heat.

Additionally the large Capacitors (2400 KVA's worth) adsorb a significant amount of reactive power created by ships fluorescent lighting, and propulsion motor inductive reactance, improving power factor to somewhat better to .9, I have plans for additional correction, as reactive power does o useful work, but consumes fuel.

You are asking about 3rd, and 5th order harmonics, therefore I assume you have a 6 pulse rectifier drive system, therefore you need filters tuned to 3rd and 5th harmonic frequencies.

Perhaps rather than dissipated as heat the energy could be recovered as DC for battery charging, could introduce other problems.

Only application I know of for ZigZag transformer connections is for three to single phase conversion, and phase shifting, any other applications, I would certainly like to hear about.

Regards

CEKM

Reply