Could somebody tell me the standard " No Load Loss " and " Full Load Copper Loss at 75 deg C, for a 10 MVA transformer working at 132 / 11 KV ?
Regards,
Rooney
India
Re: Question
06/16/2009 5:10 AM
The manufacturer can do this.
Good Answers: 5
Re: No Load Loss and Full Load Copper Loss
06/17/2009 12:43 AM
These values are an integral part of the, design and manufacturing process, and differ from manufacturer. As somebody else pointed out the manufacturer will give you the values. Normally these transformers's efficiency is between 96 and 97% at 100% load.
R T F M .......
06/21/2009 9:26 PM
For an ANSI rated txfr:
10 MVA, 132/11 kV
%Z X/R
Positive 9 15.5
Zero 9 15.5
Patriotism is the last refuge of scoundrels
08/12/2009 12:29 AM
Thank you gentlemen!!