Bus Bar Amperage

06/16/2009 5:07 AM

Hello Everybody!

Is there any chart or a website which could tell us the safe amperage (Amps) a bus bar (Aluminium) can carry with respect to its size & number?

Any help will be highly appreciated.

Regards,

Rooney

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Question2

06/16/2009 7:57 AM

No, there isn't.

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: Question2

06/16/2009 9:58 AM

Google "Copper bus bar rating"

Register to Reply
Guru
Hobbies - Musician - Engineering Fields - Chemical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jan 2007
Location: Moses Lake, WA, USA, Thulcandra - The Silent Planet (C.S. Lewis)
Posts: 4216
Good Answers: 194
#3

Re: Question2

06/16/2009 4:23 PM

http://www.electricianmath.com/neccalculations/busbarampacity.htm

Took me about 10 seconds.

You could have done the same thing and not even had to wait for an answer.

__________________
"Reason is not automatic. Those who deny it cannot be conquered by it. Do not count on them. Leave them alone." - Ayn Rand
Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#4
In reply to #3

Re: Question2

06/16/2009 5:59 PM

Regarding this, the NEC Article 366.23(A) states:

"---- The current carried continuously in bare copper bars in sheet metal auxiliary gutters shall not exceed 1.55 amperes/mm2 (1000 amperes/in.2) of cross section of the conductor. For aluminum bars, the current carried continuously shall not exceed 1.09 amperes/mm2 (700 amperes/in.2) of cross section of the conductor."

Please also see my previous answer to another thread:

http://cr4.globalspec.com/comment/384680

-MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Guru
Hobbies - Musician - Engineering Fields - Chemical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jan 2007
Location: Moses Lake, WA, USA, Thulcandra - The Silent Planet (C.S. Lewis)
Posts: 4216
Good Answers: 194
#5
In reply to #4

Re: Question2

06/16/2009 9:56 PM

Hi msamad,

Great! My main point however, was to let the OP know that the information is but a CR4 search (in your case) or a Google search away - much quicker than waiting for an answer to a post on CR4!

Cheers!

Mike

__________________
"Reason is not automatic. Those who deny it cannot be conquered by it. Do not count on them. Leave them alone." - Ayn Rand
Register to Reply
Associate

Join Date: Jun 2009
Posts: 49
#6

Re: Bus Bar Amperage

08/12/2009 12:28 AM

Thank you Gentlemen !!