Sizing Motor Feeders

06/16/2009 2:36 PM

is it necessary as per NEC to size the motor feeder 125% of full load current incase of soft starter and main breaker size shall be 225% of biggest motor full load current and sum of all fla of remaining motors?

Is it necessary to cosider starting current in sizing feeder, as it is multiple higher than the FLA, pls more information?

__________________
Engr. Syed S. Ameen
Register to Reply
Pathfinder Tags: motor protection and feeder
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Sizing Motor Feeders

06/16/2009 4:31 PM

The feeder cable shall have the ampacity of 1.25 x the FLA of the motor. The breaker may be sized at 250% of the FLA. This is not required. It could be set at a lower value. The reason is so the breaker will not trip under starting conditions. This is for 1 motor. How many motors do you have?

Register to Reply
Anonymous Poster
#2

Re: Sizing Motor Feeders

06/16/2009 11:30 PM

Short-Circuit and Ground -Fault Protection 150% to 300% NEC table 430.52

times FLC NEC tables 430.247, 248, 250 (round up next size)

Single Motor Conductors 430-22A 125% NEC tables 430.247, 248, 250

Overloads 430.32A 115%- 125% Heater (ok round up) max 140% with marked tempertuure rise of 40 degree C or less (fuse round down) type times FLA (Name

plate)

Temp rise and service factor changes can change things.

Register to Reply
Associate

Join Date: Sep 2008
Posts: 39
Good Answers: 1
#3
In reply to #2

Re: Sizing Motor Feeders

06/17/2009 4:42 AM

Its a very good answer.

where can we get the copy of NEC? Kindly throw some light on probable wesites.

Regards,

PG

Register to Reply
Participant

Join Date: Jun 2009
Posts: 3
#6
In reply to #2

Re: Sizing Motor Feeders

06/17/2009 4:00 PM

thanks for mentioning the code tables no. and for your comment

__________________
Engr. Syed S. Ameen
Register to Reply
Anonymous Poster
#4

Re: Sizing Motor Feeders

06/17/2009 8:57 AM

In sizing up feeder wire and circuit breaker in more than one motor you have to consider as per NEC Standard :

a) The full load Current according to the type of lock rotor involve

1) Squirel Cage type of rotor - 250% - 300% of the Full load current as per NEC Standard

2) Wound Type rotor - 125% -250% of Full load current as per NEC Standard

b) The size of Main Breaker (CB) - The Highest Full load ampere x the type of lock rotor of the motor plus the sum of the remaining FLA only of the

motors.

c) The size of Main Feeder - The Highest Full load ampere with lock rotor x 125% plus the sum FLA only of the remaining motors

d) For individual sizing of the motor:

1) Size of Wire - FLA x 125% round up to nearest higher size available in the table

2) Size of Circuit Breaker (CB) - FLA x the Type of lock rotor and round up to the nearest higher size available in the Table

Register to Reply Score 1 for Good Answer
Participant

Join Date: Jun 2009
Posts: 3
#5
In reply to #4

Re: Sizing Motor Feeders

06/17/2009 3:58 PM

thanks for your answer for both protection and feeder sizes as per NEC, for diffrent type of motors.

__________________
Engr. Syed S. Ameen
Register to Reply
Register to Reply 6 comments