Anonymous Poster

Sizing an Incoming Breaker

06/17/2009 9:04 AM

I have to install a Distribution Board to feed 6 no's of 2.0Tonne Split A/C unit with input power of 3kW each. The Voltage of the system is 415V/240V, 3ph/1ph, 50Hz. each AC unit is protected by a 32A, 2 pole MCB.

Now Do I size the incomer breaker solely on the (running load current + selectivity of the downstream 32A MCB) OR I need to size the incomer for (Starting current of ALL split A/C at once + slectivity)????

Early responce is highly appreciated. Thanks.

Steve51986

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator

Join Date: Nov 2008
Location: S.E. Asia
Posts: 91
Good Answers: 1
#1

Re: Sizing an Incoming Breaker

06/18/2009 9:27 AM

Steve,

I must make one assumption before I continue. It is;

1] all of the AC units are protected by "motor start" circuit breakers of the same brand & type.

If this is the case, your incoming breaker should be sized so that it does not trip under fault current conditions if any of the downstream breakers trip under fault current conditions. In order to do this, you may do 1 of 2 things;

1] contact the circuit breaker manufacturer & they should be able to answer your question.

2] consult the "time/current curves" of the downstream breakers in order to find out the characteristics of the incoming breaker.

If you don't know how to do 2], do 1].

One other thing...it's a very good idea if you know the prospective fault current of the supply circuit before you lauch into this because the circuit breaker manufacturer/distributor will probably ask you this question.

__________________
"If you try to keep a leg each side of a barbed-wire fence, you'll do yourself a mischief." - Joh Bjelke-Petersen.
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Sizing an Incoming Breaker

06/29/2009 9:57 AM

If there were to be some form of sequence start available, then the incomer needs to be sized only for up to 5 machines running and only 1 machine starting at any time. Such a start may result in economies of equipment and cables that are valuable.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856